I have following information on 120/240V loads

MOTOR STARTING + CONTINUOUS LOADS
Single phase – 120 kVA
Three phase – 51 kVA

MOTOR RUNNING + CONTINUOUS LOADS
Single phase – 104 kVA
Three phase – 12 kVA

AFTER 10 SEC (CONTINUOUS LOADS ONLY) KVA
Single phase – 97 kVA
Three phase – 6 kVA

I would like to size a transformer, which could handle this load. Assuming a unity power factor, which transformer size do you think is appropriate?

I am leaning towards a 300 kVA delta secondary padmount transformer.
Could possibly use a 225 kVA. Any suggestions? ( Primary is a 24kVY)
 

RE: TRANSFORMER SIZE

Watch out for single pad mount transformers.  They will probably have a very low single phase rating.  Your 300kVA transformer might be good for 50 or 60 kVA of single phase load.  If you want lots of single phase and a little bit of 3-phase you're better off with a bank of single phase transformers or converting your 240V loads to 208V and going with a wye secondary.

RE: TRANSFORMER SIZE

The maximum single phase loading on a three transformer bank is 2/3 of the total rating, or twice the rating of the lowest rated transformer assuming that the PU impedances and X/R ratios are equal.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: TRANSFORMER SIZE

(OP)
Bill,

That was my understanding that the mid tapped winding will carry 2/3 of the single phase load (2/3*120 =80kVA) and 1/3rd of the three phase (1/3*51 = 17kVA).
The other two windinging will take 1/3rd of both single (1/3*120 = 40kVA) and three phase loading (17kVA). However, now I am a little confused from Davidbeach's comment that a 300kVA will only serve a 50 or 60 kVA single phase load. David, where did you come up with this number?
I have not worked with padmount transformers before, but think that it would on the same principle as a bank of three single phase equal impedance transformers. Is that not correct?

 

RE: TRANSFORMER SIZE

What I remember from catalogs.  Could have changed, may be transformers designed for higher single phase loading.  Best bet is to verify with the manufacturer.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources