ceiling return plenum static pressure?

ceiling return plenum static pressure?

ceiling return plenum static pressure?

(OP)
How do you get the static pressure for ceiling return plenum when computing for the total static pressure of fan?

RE: ceiling return plenum static pressure?

Find the static pressure drop for the grille furthest from the ahu return, and any entrance into the ahu, then add about .5" and you should be fine.  If there is any return ductwork add that as well.

RE: ceiling return plenum static pressure?

(OP)
When you say find the static pressure drop for the grille furthest from AHU return duct - is that mean get the lenght from the (furthest) grille to AHU return duct and multiply by 0.1inWC/100ft (same how to get the static pressure of straight duct)?

Btw, what is 0.5in wc is that for the grille pressure drop?

Thank you for the reply.

RE: ceiling return plenum static pressure?

No, check the return grille manufacturer's data for the amount of cfm you are passing through it, they will give you the pressure drop.  The .5" is just a safety factor so you don't undersize the fan - and it will account for much of the pressure drop through the plenum itself.  Then if there is a return duct going from the plenum to the ahu, do a static pressure drop calc on that, including entrance losses and any elbows, etc.

RE: ceiling return plenum static pressure?

(OP)
Thanks, got it.

Out of topic:
What's the recommended cfm and velocity for 24x24 diffuser?

I'm using V=area x vel x %opening (70% for supply & 80% for return).

Area=24x24

I'm out from HVAC industry for 7years - thanks for understanding.

RE: ceiling return plenum static pressure?

xpsboy
At 80% opening for a 24"x24" the CFM would be about 2240 and the velocity would be about 700 FPM maxium to maintain an acceptible presure drop.  

RE: ceiling return plenum static pressure?

Back to the original question, you don't; the ceiling static is nearly negligible with respect to the system fans.
 

RE: ceiling return plenum static pressure?

Whether the plenum has a pressure loss depends strongly on the shape and construction of the plenum.

RE: ceiling return plenum static pressure?

Agreed Willard, to size your fan only on supply duct and unit static pressure could leave no room for upward adjustment should building and installation conditions merit a little extra oomph from the fan.

RE: ceiling return plenum static pressure?

Out of topic:

If I have straight duct with VAV on it, if I will compute for the total static pressure of straight duct - do i need to add the static pressure of VAV (coil/box/etc) up to the supply diffuser or just at the entry of VAV box? So from the VAV supply duct to the supply diffuser will take care of TSP of VAV (not the AHUs TSP)?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources