Overload of 3 phase rectifier

Overload of 3 phase rectifier

Overload of 3 phase rectifier

(OP)
I would like to know from someone if an incoming phase is burnt off will a three phase rectifier continue to operate and will this cause the rectifier to go into over load. Recently we had a phase failure and the rectifier diodes popped.

I know in a three phase induction motor, if the motor looses a phase, it continues to operate however if the motor is stopped and restarted, it movement operate.

Does a similar thing happen to a rectifier.
Specifications of rectifier:
Input voltage : 3.3kV
Output voltage: 3kV direct current


RE: Overload of 3 phase rectifier

Loss of one incoming phase on a 3-phase rectifier will result in the remaining two phases increasing to approximately 173% of full load current, assuming the output of the bridge remains constant.  The remaining two phases will operate as a single-phase bridge rectifier.  The ripple will increase noticeably also from the normal 3-phase operation.

RE: Overload of 3 phase rectifier

Tell me I'm wrong...but your voltage will drop too!

RE: Overload of 3 phase rectifier

(OP)
jwertman, how do you arrive at the figure of 173% full load current?

RE: Overload of 3 phase rectifier

For 3-phase supply, the input line current would be:

I(3phase)= P/(V x sqrt(3))

For the same output power, with 1-phase supply, the input line current would be:

I(single phase) = P/V

I(single phase)/I(3phase) = sqrt(3)

It's the same situation as single-phasing a 3-phase motor.  This assumes that the DC load is the same on the output.  The output voltage may drop, and if it does then the output power would also be reduced and the input current would be less.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources