Select for dehumidification or cooling?

Select for dehumidification or cooling?

Select for dehumidification or cooling?

(OP)
Does anyone know what criteria to use to select an air handler for either cooling or dehumidification?  I used two design conditions using ASHRAE Fundamentals handbook.
Thanks

RE: Select for dehumidification or cooling?

Familiarize yourself with sensible and latent cooling components of air system cooling loads.

High sensible loads = lots of air and shallow coils
High latent loads = less air and deeper coils

RE: Select for dehumidification or cooling?

(OP)
If I use the selection for the hottest day, the sensible load will be satisfied, but the latent load.  If I use the most humid day selection, the latent load will be satisfied, but not the sensible.

RE: Select for dehumidification or cooling?

How far apart are the two design conditions and how different an equipment selection do they drive?

Remember that the ASHRAE design conditions aren't necessarily "real".  They result from a lot of statistical mumbo-jumbo over a large number of years of data.

Use an hourly data set like TMY and see how many hours per year each equipment selection will operate in an unsatisfactory way.  Maybe tweak the selection a bit and try again.

It's an engineering judgement thing.   

RE: Select for dehumidification or cooling?

Why not satisfy both?  Grab a psych chart and get your capacity the old fashioned way.  Use the design day Dry bulb and design RH, get your enthalpy from that then use Qt=cfm*4.5*deltaH

RE: Select for dehumidification or cooling?

(OP)
What I did is choose the most humid day selection, since it resulted in a large load by 30 MBH.  I kept the hottest day airflow and used it with the higher load.  My system has a reheat coil, so I won't sub-cool the space.
Thanks for the help.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources