single line to ground fault

single line to ground fault

single line to ground fault

(OP)
While doing the arc flash study, I wonder what effect does the single line to ground fault has on arc flash current and incident energy?

When I performed the arc flash study, I did a mistake of low resistance grounding the transformer and generator instead of solidly grounding them. There was no effect on 3phase current. But single line to ground fault current changed drastically when I changed the grounding to solid. What effect does that have on arc flash?

RE: single line to ground fault

duuh!

RE: single line to ground fault

None what so ever.  

RE: single line to ground fault

Depends. If you never have a fault, then all this arc-flash stuff hasen't helped you.

RE: single line to ground fault

The IEEE 1584 method for arc-flash calculations is based entirely on three-phase faults on three-phase systems.  This generally going to be the worst-case, so line to ground faults don't enter into the picture.  

 

David Castor
www.cvoes.com

RE: single line to ground fault

(OP)
Thanks everyone!!
Hi dpc...
I am using NFPA calculation. So is it going to  change the arc flash. If not, why are we doing the single line to fault calculation?  

RE: single line to ground fault

Same approach - three-phase faults only.  

 

David Castor
www.cvoes.com

RE: single line to ground fault

You may need single line-to-ground faults for coordination, but not for arc flash.
 

RE: single line to ground fault

As far as I know, 3 phase fault current calculation is overcurrent relay setting.Meanwhile single phase fault is earth fault relay setting.

Correct me if i wrong.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources