Expansion Joint in 150Æx300Æ building

Expansion Joint in 150Æx300Æ building

Expansion Joint in 150Æx300Æ building

(OP)
I have a new building, 3 stories, 150' wide x 300' long in Midwest region. Framing is going to be composite steel, with precast wall panels and lot of curtain wall. In the past I have used a thumb rule of 250' as the maximum length one can use before needing an expansion joint. But obviously if I can get away without putting an EJ in the building, I would love to do that. What length would you recommend before considering an EJ?

Thanks,
 

RE: Expansion Joint in 150Æx300Æ building

Depending on geometry, climate and materials of construction, you should be able to do 300' (an arbitrary limit of mine).  You will have joints in the exterior due to precast construction and the interior will be a uniform temperature.

If you are uncomfortable with 300', then cutting the building into 2 - 150'x150' is also a good idea; they are the right aspect ratio.

Dik

RE: Expansion Joint in 150Æx300Æ building

kind of agree dik

RE: Expansion Joint in 150Æx300Æ building

Your best bet is to do a volume change calculation.  For a 150' length you could approach a 3/4+" delta (the roof will see a lot more).  However, with a flexible system, the distribution of the volume change can be distributed to joints and connections.   

RE: Expansion Joint in 150Æx300Æ building

(OP)
Whose responsibility is it ultimately to determine if the building should have an exp jt, Arch or Engr?

RE: Expansion Joint in 150Æx300Æ building

whom ever is on the line for fixing cracked floors, drywall, windows ets smile  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources