I have a motor 4kW, DOL Start, with a Telemechanique  GV2ME14 Motor Circuit Breaker.
The motor an ATEX rated Motor and is installed in ATEX Zone 2 area.
The motor manual is not clear on whether the Thermistor has to be wired if the motor is not fed from an inverter. I have emailed the manufacturer and am waiting for a response.
In a non hazardous area I would typically not use thermistor protection on a DOL Motor, but I would use a thermistor if the motor is fed by an VFD.
Similarly I would definitely use a Thermistor on a VFD fed motor in a Hazardous area.
However I am not sure if it is needed for a DOL fed motor. The fan should be more than capable of keeping the motor below the rated temperature, however if there was damage to the motor fan, or the intake was blocked it would be conceivable that the motor could heat up but the Motor protection would not trip.
 

RE: DOL motors & Thermistors

It doesn't have to be wired.

You may want to wire it and use the added protection for the motor.

RE: DOL motors & Thermistors

There are separate Thermistor Tripping Relays for this situation. I'm by no means an IEC expert, but I seem to recall that maybe the Thermistor is required in some ATEX zone classifications. But don't go by me, I could be totally wrong, it may just be that IF you are going to use a Thermistor Trip Relay it too must be ATEX certified.

"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)
  
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies  

RE: DOL motors & Thermistors

If the motor is DOL then I think it will be code compliant. If you used it with a VFD then you would require the thermistor protection to be implemented. I don't know where you are, so difficult to be more specific.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources