Column strip width ACI-318-08 13.2.1

Column strip width ACI-318-08 13.2.1

Column strip width ACI-318-08 13.2.1

(OP)
"Column strip is a design strip with a width on
each side of a column centerline equal to  0.25xl2 or
0.25xl1, whichever is less."

¿What happens when L1 is shorter than L2 but L1 is not equal in successive spans? ¿Should I use variable column strip width? In this case, ¿what would be the width of the negative reinforcement on the column?

RE: Column strip width ACI-318-08 13.2.1

If there is only a minor variation in the spans, say 20% or less, I would make the column strip width equal to  1/2 the shorter span and carry that width right through.   

RE: Column strip width ACI-318-08 13.2.1

This reveals the reason why irregular bays are not the best for two way slab systems.  Not to say they don't work - just makes the Direct Design or Equivalent Frame approach less "reasonable".

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources