what is the purpose of "Neutral Reactor" and "phase shift transformer" in a substation?

RE: Neutral Reactor and phase shift transformer

These links have some good basic explanations. Did you have specific questions about either one?

Neutral reactors are fairly common.  "Phase shifting transformers" are fairly rare, assuming you don't mean the normal phase angle shift do to the specific transformer connection such as 30 degrees for a delta/wye transformer.

http://en.wikipedia.org/wiki/Quadrature_booster

http://lmgtfy.com/?q=Neutral+Reactor

RE: Neutral Reactor and phase shift transformer

PST and QB although very similar, not the same thing with different names, like wikipedia definition might lead to

May you grow up to be righteous, may you grow up to be true...

RE: Neutral Reactor and phase shift transformer

Hello Steve14,
neutral reactors are installed in order to modify the zero sequence impedance of the system in that node. They are quite common in Europe in medium voltage networks (petersen coils). In the HV and EHV networks they are less common; I think here in Italy there is only a couple of them connected between the neutral point of a single phase  shunt reactors bank installed at the end of a mixed aerial-cable 400 kV line.
PSTs are used to control power flow along the lines to which they are connected to. In Europe they are not so rare, there are several 400 kV PSTs up to 1800 MVA, often installed on interconnection lines.
Phase shifter transformers windings arrangement differs from quadrature boosters. The latter modify both phase and amplitude, while symmetrical PSTs change only the phase of the voltage.
    

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources