Fire Rating for Roof Assembly

Fire Rating for Roof Assembly

Fire Rating for Roof Assembly

(OP)
Where might one find a tested assembly for a concrete slab or a hollow core plank roof deck with polyiso insulation and EPDM roof membrane (no ceiling).  This seems like a pretty basic assembly, but I can't find anything in the UL Classifications.  
 
For a plain 6" slab, Table 720.1 (2009 IBC) lists up to ~3-hour rating, but then Section 720.1 says "Where materials that change the capacity for heat disipation are incorporated . . . fire test results or other substantiating data shall be made available to the building official to show that the required fir-resistance-rating time period is not reduced."  
 
Does anyone know if this data exists for this seemingly simple assembly?
 
Thanks for any assiatance.
 
 

RE: Fire Rating for Roof Assembly

I need help understanding this. The IBC doesn't require fire-rated roofs. It does require roof covernings that are ignition-resistant.

Are we talking about a horizontal assembly or are you talking about roof coverings?

RE: Fire Rating for Roof Assembly

(OP)
I am looking for a horizontal assembly.

RE: Fire Rating for Roof Assembly

Then JAE answered your question. You can also design the horizontal assembly to the prescriptive requirements in IBC 720.1(3).

RE: Fire Rating for Roof Assembly

(OP)
As I noted in my original post, I have looked into the UL Classifications, but cannot find a UL assembly consisting of a concrete slab with insulation on top. I would think this would not be an unusual construction.  IBC Table 720.1(3) shows a ~6 inch slab will provide a 3-hour rating, but the last sentence in Section 720.1 seems to preclude the use of the slab with insulation without additional testing.  I was hoping to find some alternate test reference for what seems like a straight-forward assembly.

It seems absurd that even if I use 4-foot thick roof slab, the building code will not permit it for a rated assembly of any duration if I put just an inch of insulation on top.

RE: Fire Rating for Roof Assembly

Have you considered performing calculations in accordance with IBC Section 721 to determine the estimated fire-resistance of the horizontal assembly? It is possible your assembly would meet these requirements.

RE: Fire Rating for Roof Assembly

(OP)
The only means I see in that section is 721.2.2.3 which requires the use of insulating concrete or mineral board for insulation along with built-up roofing. In order to meet the Energy Code, I would need 8-12 inches of board insulation (8 to 12 layers of 1" board). This puzzles me, because this would provide the same insulating value that I want to provide using polyiso, which Section 720.1 says may reduce the rating.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources