ABB-REG670 voltage protection(60) and fuse failure(RFUF)
ABB-REG670 voltage protection(60) and fuse failure(RFUF)
(OP)
Does anyone knows the difference in the of application of Voltage differential protection (PTOV, 60) and Fuse failure supervision (RFUF)?
It seems samething.
It seems samething.






RE: ABB-REG670 voltage protection(60) and fuse failure(RFUF)
Its not same, differnt pinciple of operation and not only for REG670
function 60 is volatge phase differntial protection and two VT on the bus/line are needed.
FFS is voltage/curent function, operated on the U2/I2 or U0/IO or both of them principal.
Hope that help.
RE: ABB-REG670 voltage protection(60) and fuse failure(RFUF)
I am talking about difference in the application, not principle of operation.
RE: ABB-REG670 voltage protection(60) and fuse failure(RFUF)
Yep, application is a same.
RE: ABB-REG670 voltage protection(60) and fuse failure(RFUF)
REG670- function FFS block functions 40, 21, 27, etc
REG670-function 60 does not.
RE: ABB-REG670 voltage protection(60) and fuse failure(RFUF)
its free programmable in the PCM600
depend on your standards
RE: ABB-REG670 voltage protection(60) and fuse failure(RFUF)
Issued: December 2007
Revision: B
IED product version: 1.1
RE: ABB-REG670 voltage protection(60) and fuse failure(RFUF)
Can't you just set it up to block the functions you want under signal matrix?
RE: ABB-REG670 voltage protection(60) and fuse failure(RFUF)
I'm not familiar with the REG670 to answer you.
I always saw 60 function blocking those functions 21.40, ...
I wonder what is the advantage of using 60 or FFS to block functions 40, 21, 27.
RE: ABB-REG670 voltage protection(60) and fuse failure(RFUF)
No advantages, its used, when you not have a second VT.
ActualLy, 60 is best solution.
Of course possible do it (if it prepared) in the single matrix.
RE: ABB-REG670 voltage protection(60) and fuse failure(RFUF)
This paper has some good information about the topic.