hydrostatic testing of water pipes

hydrostatic testing of water pipes

hydrostatic testing of water pipes

(OP)
Normally hydrostatic testing for chilled water/heating hot water distribution system is specified, to be tested at 1.5 times of working pressure.  Is pneumatic test pressure (150 psig) in lieu of hydrostatic test acceptable?  Which code governs for testing of chilled/hot water piping?

RE: hydrostatic testing of water pipes

I think better place for this question is"piping &fluid mechanics engineering".This forum also has some active "responder"

RE: hydrostatic testing of water pipes

bansi,

The place to find answers to your question is the piping code that the system is to be designed to (typically ASME B31.3 or B31.1)

Both codes allow pneumatic testing of systems, but only allow this type of testing when hydrostatic testing is "not practical" ( read: filling with or water residue would cause problems)

Typically, this type of test is reserved for low pressure designed systems (up to about 75 psig) or for large diameter, thin walled systems, where additional bracing and support would be required for hydrostatic testing

You should be aware of the dangers of this type of testing..... they are described in several of the piping related websites.

Hope that this helps


MJC

RE: hydrostatic testing of water pipes

Other responders have correctly pointed to the codes and more active links.
I would like to add two cautions:
1) Typically, the codes require pneumatic testing at higher pressures than hydraulic testing, e.g., 150% of maximum working pressure for hydraulic testing, but 200% for pneumatic testing
2) Be careful with certain materials. I have seen catlogs from PVC pipe manufacturers that warn that no pneumatic testing should be done.

RE: hydrostatic testing of water pipes

skhungar,

are u sure for pneumatic test is 2.0 X design pressure not 1.1 time.  

RE: hydrostatic testing of water pipes

Whoa !!!

Pneumatic testing definitely must NOT be 200% of design pressure!!  Read the code, and get someone familiar with the technology first.

When you hydrotest ( 1.5* design pressure in some codes, 1.3 times in other codes) , the worst eventuality if athe vessel fails is collapse of the vessel , but during a pnuematic test, the failure of the vessel is a catastrophic explosion. For that reason, all such testing must be above 70 F fluid and vessel temp and warmer than the documented ductile brittle transition temperature, and the pnuematic test pressure is usually to a max of 1.1 to 1.2 times  design pressure.

Better recall the prior message before someone gets hurt.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources