I know there is an simple answer to this ... at least I think so.
I have a sterilizer that can accept a steam pressure range of 30 psig to 80 psig. The required flow rate at 30 psig is 200 Lbs/hr, and the flow at 80 psig is 300 lbs/hr. Seems like it should be the other way around.
What am I missing?
I have a sterilizer that can accept a steam pressure range of 30 psig to 80 psig. The required flow rate at 30 psig is 200 Lbs/hr, and the flow at 80 psig is 300 lbs/hr. Seems like it should be the other way around.
What am I missing?





RE: Heat Exchanger Steam flow rate versus pressure
In your specific case, at 30 psig the specific enthalpy of evaporation is approx 929 Btu/lb, while at 80 psig it is approx 892 Btu/lb. Anyway the flow rate required should only increase by a 4% and not by 50%, so your figures are quite odd.
RE: Heat Exchanger Steam flow rate versus pressure
How is the steam flow rate measured? Is the sterilizer at atmospheric pressure?
RE: Heat Exchanger Steam flow rate versus pressure
RE: Heat Exchanger Steam flow rate versus pressure
The manufacturer is probably telling that, if needed, the pressure and the heat duty could be increased.
RE: Heat Exchanger Steam flow rate versus pressure