Shield ungrounded, what about armour?

Shield ungrounded, what about armour?

Shield ungrounded, what about armour?

(OP)
Hi

I have a lenght of 3C 25kV TECK power cable in a substation.

If I decide to do not ground the shield on one side of the cable what do I do with the aluminum armour with the connector?

It should remain ungrounded as well isn't it?

Someone can confirm what is the right way to do it?

Thanks

RE: Shield ungrounded, what about armour?

a) Consult an expert familiar with regulations in your area.

b) They will likely tell you to bond the shield and the armor together and to ground to earth at one end only.

c) Depending on GPR in your substn and fault currents that may exist on the cable,  you MAY require an arrestor/shunt  at the UNGROUNDED end to dissipate transient overvoltages.

RE: Shield ungrounded, what about armour?

According to IEEE-575-1993 the armor [like the shield] should be solidly grounded at one or more points:.
"Cable shields and metallic sheath/armor should be solidly grounded at one or more points so that they operate at or near ground voltage at all times".
See IEEE-575-1993 ch.6.2 High-voltage power cable 6.2.4 Grounding practices.
A 3 core cable shield or armor losses are negligible if it is both ends grounded.
So, if there is not any other reason to avoid armor grounding you have to ground it.......
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources