I need to implement capacitors to improve power factor im my factory. there are 50% of AC motors, and the rest are DC.

01. which is more effective in following 2?
  # implementing capacitor bank for the whole system   or
  # implementing individual capacitors for AC motors only.

02. What i Thyristor Control?

03. Pro's and Con's in using Capacitor bank and Thyristor Control.

RE: Capacitor bank

It's impossible to recommend the way to do it considering the lack of information and the fact it would need to be studied in detail.

I will say that any power factor capacitor banks may need special attention due to the potential for harmonics from the thyristor controls. De-tuning reactors and higher voltage rated caps may be necessary.
 

RE: Capacitor bank

Your first choice, or the "low hanging fruit", will be larger AC across-the-line (atl) started motors with 0.8 power factor.
Beyond that, the addition of pf correction caps in any electrical system needs to pay attention to harmonics that could cause problems.
And I shouldn't even make the blanket statement that the 0.8 pf atl motors are a safe bet for improvement because if the environment is dirty enough with harmomnics, it could still be problematic.
It really comes down to a requirement to model the system to account for THD, and pf correct accordingly, perhaps with tuner caps if required. But they're so expensive that they compromise the payback period.
PF correction is no longer routine, as it was prior to the prevalence of harmonics.
John M

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources