Large Motor Grounding
Large Motor Grounding
(OP)
I have a motor grounding question. Our specifications state that large motors should have grounding pads on both sides. This particular application is for a 2000HP 4160v motor. We have two size 500 ground wires going there, but this motor came with only one grounding pad in one side. I couldn't find anything in the NEC book regarding the 2 sides requirement, but would a single 500 size cable connected to only one side of the motor frame be sufficient in this application? Thank you for your help...





RE: Large Motor Grounding
RE: Large Motor Grounding
The two ground pads are more of a belt and suspenders thing than a physical necessity.
The equipment grounding conductor that is run with the phase conductors will provide the lowest impedance return path anyway.
Make sure to ask the motor supplier for a credit.
David Castor
www.cvoes.com
RE: Large Motor Grounding
From an NEC standpoint I believe all that is required is the equipment ground conductor and that this EGC will carry most of the fault current as dpc mentions. I dont believe a connection to earth is required on a motor but I've seen it done in several cases as a supplimentary protection.
dpc brings up a good point about the 4160 system being resistance grounded. How much would this HRG system limit the step potential at the motor compared to a solidly grounded system? I guess this would be a funcion of the reduced fault current that would flow. In the HRG case would the wire between the motor frame and earth even do anything to limit touch potential if most of the current flows through the EGC?
RE: Large Motor Grounding
RE: Large Motor Grounding
As we all know, terminal boxes are always the wrong side and motors always rotate the wrong way on start up!