Hilti HY-150 with SS rods
Is this the recommended  anchor in exterior application (in existing concrete)? It will be exposed to temp and weather.
RE: Hilti HY-150 with SS rods
Yes.  Routinely used.
Thanks Ron.
Now the other question I have is, how do you define cracked conc vs non-c?
I use the Hilti Hy-150 all the time with either stainless steel rod or the Hilti TZ anchors... slikker than doggie poop...
Dik
For cracked / un-cracked you can look at the location and moment diagram of the member you are fixing to (i.e. on a continuous beam cracked at mid-span bottom or at supports top). Alternatively use cracked by default, as this will be a worse case option.
I usually switch the SS with all threaded hot dipped galvanized Rods.  Buy in 10 ft lengths and cut to length.  Reduce cost.
Wouldn't those cut-off rods rust at the cuts where galv. has been chopped off?
Any exposed steel through cuts and field welding get repaired with galvanize repair paint. Of course if the environment calls for SS then it should be used.
One trick to cutting all threads and not damaging the threads is to pre load them with nuts.  after cut is made remove the nut and it will self aline the thread if damaged.
We default to all concrete as being cracked.