ISA/IEC control valve specific heat ratio

ISA/IEC control valve specific heat ratio

ISA/IEC control valve specific heat ratio

(OP)
All,
ISA 75.01 and IEC 60534 use the "specific heat ratio" for control valve sizing.  Does this "specific heat ratio" mean the ideal gas specific heat ratio (evaluated by k = Cp (Cp-R) ) or does it mean the actual isentropic exponent (same isentropic exponent used in orifice sizing and relief valve sizing)?   There does not seem to be any definitive answer in the the ISA or IEC specifications.  Some control valve vendors use isentropic exponent while other vendors use ideal gas specific heat ratio.   The values are very different when the gas is near the critical point or supercritical.
 

RE: ISA/IEC control valve specific heat ratio

(OP)
hsbcn,
Thanks for the link.   Yes, I have a copy of this.  Unfortunately it does not state how to calculate the "actual specific heat ratio".  Note that the "actual" specific heat ratio mentioned in the link and the isentropic exponent are not the same value.   

RE: ISA/IEC control valve specific heat ratio

The specific heat ratio for ideal gas is "incidentally"  the same as that the isentropic exponent.
Glance at http://webbook.nist.gov/chemistry/fluid/ to find fluid properties over a wide range of temperatures and pressures (even in the supercritical region). You'll find there cp and cv values for specific given conditions and this will allow you to calculate the specific heat ratio required for the sizing procedure.

RE: ISA/IEC control valve specific heat ratio

(OP)
ione,
Thanks for the info.   However, the issue here is not how to determine the specific heat ratio.   Rather,  what is the required "specific heat ratio" to be used for the ISA/IEC sizing equations (ie. is it ideal gas specific heat ratio, isentropic exponent, or even real gas specific heat ratio ?).   

RE: ISA/IEC control valve specific heat ratio

You've to take into account the specific heat ratio, and more specifically the actual specific heat ratio. When ideal gas behaviour is not a reasonable assumption for your scenario (i.e. supercritical fluids) compute the specific heat ratio for the actual conditions.

Look better at page 16 of the link provided by hsbcn

http://www.dressermasoneilan.com/documents/LiteratureLibrary/tech-docs/eng-data/OZ1000-0304-0509-web.pdf


 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources