(OP)
Do we traditionally install a Multifunction Protection Relay on a Low Voltage MCCB? Will it operate like a Power Circuit Breaker from a Protection Relay?

Thanks

RE: Multi Function Protection Relays for MCCB

Quote:

Do we traditionally install a Multifunction Protection Relay on a Low Voltage MCCB?

No.

Quote:

Will it operate like a Power Circuit Breaker from a Protection Relay

The MCCB can be tripped by a protective relay (or any contact) only if it has an optional shunt trip coil.  

 

David Castor
www.cvoes.com

RE: Multi Function Protection Relays for MCCB

In most applications, the external protective relay comes off as overkill.  However, there are some cases where the coordination of protection requires settings not available in the integral trip unit.

Most manufacturers sell shunt trip units for their breakers.

old field guy

RE: Multi Function Protection Relays for MCCB

MCCBs don't have a withstand rating, so instantaneous cannot be disabled when applying an external relay.
 

RE: Multi Function Protection Relays for MCCB

Quote (jghrist):

MCCBs don't have a withstand rating, so instantaneous cannot be disabled when applying an external relay.

True, but not always obvious.  In part it depends where the hybrid Insulated Case Circuit Breaker falls.  There are families of MCCB/ICCB breakers where it appears possible to turn off the instantaneous trip.  What happens is that there is also an Instantaneous Override trip that isn't always clearly obvious in the documentation that will trip the breaker at its fixed setting.  This fixed setting may be relatively high and of not much concern, or it may be surprising low and not much above the highest instantaneous setting.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources