Hi All,

We are planning of installing three(3)- single-phase,25kVA, 13.8kV/600V, pri- Delta and sec- wye-grounded pole-mounted transformer for our system. For protection on the primary-side of the transformer, I was wondering if I should spec out a self-protected transformer in which the surge arrester comes as an integral part of the transformer or to have both the transformer and distribution class surge arrester as two seperate entities.

I'm sure there are pros and cons with each design but I would like to go with the standard recommendations of NEC or CEC.

Comments and thoughts, pls

Regards,

Sonic

RE: Surge Arrester

Nothing in NEC is going to address this decision.  

My suggestion is to use a standard transformer and mount a standard arrester as close as possible.  The self-protected transformer will be much more difficult to replace in the future if one should fail.

 

David Castor
www.cvoes.com

RE: Surge Arrester

Most CSP transformers are single-bushing and not appropriate for delta connection.  The utilities that I'm familiar with use conventional transformers for 3Ø banks.
 

RE: Surge Arrester

I have seen some utility specify transformer -230/69kV  Pri-wye-grounded and sec-delta, including surge arrester to be installed on top of the tank, connected to 230kV bushings.
   

RE: Surge Arrester

If the surge arrestor is built into the transformer, it is required to determine if additional surge protection is needed on the secondary.
This will depend on the size and importance of the transformer and also the cost and type of arrester. You seems to be using distribution class arrester (inexpensive) which has a very low lightning impulse value compared to station (expensive) and intermediate class arresters.

I would agree with what dpc suggested....the surge arrester should be mounted as close as possible to the transformer terminals, preferably within 1 meter and on the load side of the incoming switch.

However, NEC talks only the briefs of surge arrester under article 280 but does not talk about application on transformers.

Regards
Santosh

RE: Surge Arrester

(OP)
Thank you all for the comments.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources