Sloped roof acting as a diaphram
How does a sloped,sheeted roof (roof trusses 4:12 +/-) relate to the classic diaphragm modle which is presented as horizontal beam with roof edges acting as chords and the sheeting acting as the web. The picture I see is a flanged beam with a large buckle in the middle and I have difficulty expecting that this condition can replace a flat horizontal diaphragm provided by sheeting the underside of the trusses.
RE: Sloped roof acting as a diaphram
Draw a cross section through the ext. wall and the roof truss, a free body diagram (FBD). How is the wind load resisted by the roof diaphragm? In any event you must get the wind load from the wall, through the double top pl. into each truss, and then into the sheathing diaphragm and maybe partially into a diaphragm caused by clg. sht.rk. We know the sht.rk. absorbed considerable load or energy before roof failure, but are just recently being allowed to consider the affects of osb sheathing, plus sht.rk., because their shear stiffness is so different. And finally, a well blocked and designed diaphragm takes these loads out the end shear walls or gable end walls.
You claim to understand the flat (horiz.) roof as a concept to do the above. The diaphragm doesn't act differently when it is inclined, but the magnitude of the loads and the way the loads are input does. A 4:12 roof is still pretty efficient at transferring these lateral loads through diaphragm action, draw the FBD right at the double top pl. and truss seat and sheathing. What are the load components into the truss and sheathing and truss hold down, etc? Why do you need truss hold down hardware, other than for suction loads (uplift), what about blocking btwn. trusses and the top pls. and sheathing under the various slopes. The 12:12 roof is not nearly as efficient and the load components are much different; and a mansard roof is almost useless w.r.t. this lateral loading, where you would need (want) a moment connection btwn. the top pls./studs and the truss to assist in resisting this lateral loading.
The diaphragm acts the same, it doesn't know the difference re: flat or inclined, but the loads and their magnitude and the exact way they are input changes; thus the need for added attention to hold down hardware, chord or shear transfer blocking at the top pls., trusses and sheathing. And, blocking and shear transfer and special attention to the framing and bracing on the gable walls may be important too.
Sometimes, continuous venting is required at the ridge line. That means the diaphragms are separated by two or three inches. There should be a continuous chord member each side of the vent, but it does not seem to be common practice to provide one.
BA
Mike McCann
MMC Engineering
http://www.eng-tips.com/viewthread.cfm?qid=178730
The problem is, nobody is quite sure of how the diaphragm behaves.
BA
Mike McCann
MMC Engineering
In order to model it, you need to tell the program whether or not the two roof plates are tied together at the ridge line.
In the absence of a ridge vent, I think you could tie each plate to a continuous ridge member. In that case I believe the two plates will tend to act as one and there will be no need for a chord member at the ridge.
If the two plates are separated, they will tend to act as two separate diaphragms and would need another chord member each side of the the vent opening.
BA
Perhaps this would be a good topic for someone's Masters Thesis.
Mike McCann
MMC Engineering
The need for proper diaphragm chord blocking and also blocking to distribute the shear flows over shear walls is absolutely essential, and Mike give a good explanation of this in that thread, as I recall. Proper attachment at each detail level is also essential. The effectiveness of the diaphragm in reacting lateral loads was left somewhat in question as it relates to the slope of the diaphragm. If someone has access to RISA 3D and would model this problem and run it, I for one would love to see the results, at a few different slopes. I believe that what I said in my post above would hold true. I think, on a typical residential roof, the rafter and certainly the truss is the primary bending resisting member and that the osb sheathing is the diaphragm element, as long as rafters and blocking keep the diaphragm from buckling, and properly transmit the load components up into the diaphragm. What I have always had trouble putting my finger on is; when the beam/column action of the rafter starts to become dominant, and when the diaphragm action becomes ineffective, or too small to count on, and instead you need the moment connection btwn. the rafter and double top pl./stud to pick up the lateral load at the top pls. At lower slopes or a flat (horiz.) roof we have no problem with this, at slopes around 10:12 and greater, I start to have my doubts, even though the rafter thrust is decreasing.
I think the reason BA's text books, and mine, don't cover this sloped diaphragm issue is because our text books are so darn old. Our text books were made of virgin wood as was our sawn lumber. They are from an era when engineers, architects and builders thought rafter ties were a good idea and only the architects didn't understand why. Furthermore, some of our texts mention plywood as a new fangled manuf'ed. product of dubious parentage. We understood that diagonal ship lap sheathing was better than horiz. laid sheathing. I'm partly kidding, because my earlier texts do cover plywood diaphragms, but we sure weren't stressing them like we want to today. Maybe I should not be speaking for BA, but I'll bet I'm not too far off. Then, in the earlier thread BA suggested that the sloped roof diaphragm system might be looked at like a folded plate system, but now he puts the lie to that by asking the question of what happens when is often the case, that the sheathing isn't nailed to the ridge beam/board or, worse yet, when you have a 3" gap at the ridge for venting. And, nobody wants chord blocking up there either because it interferes with the venting. As has been said a number of times, the blocking at the ridge and double top pl. at the ext. wall isn't even provided. And, I guess the explanation for that working is that on a typical residential roof the diaphragm proportions don't require serious sheathing joint blocking or chord design to function under reasonable loadings.
While we don't encourage student posting of homework problems on this forum, I would encourage a grad. student who was looking for a thesis problem to tackle this assignment with our help, and publish the results. I suspect some of the wood products people have looked at this if we would dig deep enough. And, as I post I see that Mike has stolen my thunder, here.
Flat or inclined diaphragms (i.e. monoslope) I can visualize. It is the gable roof with the extreme pitch break at the ridge that is foggy to me. How does in-plane load in the sheathing transfer across the ridge without inducing some vertical load in the rafters or trusses?
That sheathing has a lot of mysterious effects on the behavior of wood framed roofs - particularly stick-framed roofs.
But I am sure they work good enough - the forces transverse through the top chords of the lumber. Not exactly allowed - but probably OK.
Probably could never show it good on paper....
But then I remember an old experiment where they took a brand new house - loaded it up to code and started cutting.
They removed almost two-thirds of the roof members before they got a failure. Interesting....
Now since windward pressure is more than negative leeward, there will be an imbalance, which I would opine is resisted by the trusses. Even though they were not designed for this type of force, trusses in general are well suited for this type of brace since they usually have a flat bottom chord with a diaphragm of sorts (ceiling), braced to chord, and internal webs. This will be a short duration load, and in my guesstimation would result in less internal stresses than a full code dead + live load combination.
When wind loading is parallel to the ridge, in theory the ridge will be at the zero-shear area of the diaphragm. So a ridge vent in this loading scenario shouldn't have much affect whatsoever.
Of course in practice, nobody builds ranches anymore. Having done LOTS of roof inspections in Florida, anything built in the last 10-15 years has a slew of hips, valleys, dormers, etc. forced upon it by pseudo-designers, not even architects, who think that makes the house pretty... So how do these roof diaphragms perform? Well, most of them are not designed by an engineer so who knows what people are doing in these instances. There are so many unintended redundancies in a residential structure, like Mike said. I have seen fire and wind damaged buildings whose roof systems were still largely intact despite several damaged or missing trusses, walls, etc. Like Dave said, an FEA model of some roof systems would be very interesting, amazingly all of the parts and pieces probably "just work", even if we can't sharpen our pencils and show where every last pound of force is resolved.
And frankly, until all residential building construction is up to snuff (ie load path and connections), I don't think we will find out, because a roof diaphragm is the last thing I expect to fail in WIND country. Too many other things will fail first- windows, doors, sections of plywood, uplift connections, etc...
Seismic is another issue, and I wouldn't be surprised in the right scenario if this controls, since the other lateral and uplift forces are largely not a factor unlike in a wind event.
But I doubt we will see any research into this until we get a body count, hate to say that but...
2nd, the amount of fog surrounding 98% of the engineering community on the topic of how roof vents effect sloped roof diaphragm behavior is amazing as well. Ventilation is a real deal. Many of us have seen moldy, saturated i.e decayed roof systems because of lack of proper ventilation. But how many of us have seen a roof diaphragm fail because a ridge vent was installed?
Sorry for lack of input. Just some observations. Good post.
I have used a ceiling diaphragm a couple of times. Once in a gable roof with probably a 12:12 pitch, once I drew a couple of diagonal braces to scale and then explained this conundrum to the architect, that had no problem with it.
Hokie- Down under do you use gyp board as your diaphragm or sheath it first and then cover with gyp? And I assume this is done before the interior walls are framed, otherwise that would be some very tedious carpentry ala plywood jigsaw puzzle...
I won't use gyp board as a diaphragm after doing hurricane forensics in 2004 and saw what moisture does to gyp board. In the extreme case that summer some areas got hit with 3 hurricanes within a couple of months and numerous power outages. A small leak in your roof can ruin your gyp board diaphragm.
Bigmig- ZERO roof vent diaphragm-related failures, EVER! Well, show me the pictures if they are out there :)
The first has to do with horizontal shear as from EQ or wind forces. With a diaphragm of equal size to either side of the ridge, the shear forces in the diaphragm should be zero at the ridge anyway. But for unequal diaphragms, there will be a shear value to develop which can be detailed, even with the venting.
The second scenario has to do with the sloping roof diaphragm supporting vertical loads. In this scenario, it makes no matter whether or not there is a ridge vent that breaks the continuity or not. Each diaphragm to either side of the ridge will take it's own portion of the vertical load depending on their relative stiffnesses. It's just as BA brought out earlier that the chord force heeds to be developed through blocking and strapping.
Thoughts?
Mike McCann
MMC Engineering
There are a variety of solutions, but yes, the gypsum board is recognized as one method. Sometimes diagonal bracing is used, occasionally plywood or fibre cement board as a diaphragm. But the ceilings go in after everything is framed, so the diaphragms only span between bracing walls. The interior partitions are used as bracing walls as required. Typically the bracing walls have plywood or fibre cement bracing panels, with gypsum board overlayed. We typically only have ribbed steel roofing or concrete/clay tiled roofs, with sarking under the roofing. No continuous sheathing.
I don't think that is correct. When wind pressure is applied normal to the ridge line, the diaphragm shear along the ridge varies linearly from a maximum at the gable walls to zero at midspan. In the absence of blocking, the shear must be resisted by the top chords of the trusses because there is nothing else available. The plywood panels are not connected to each other.
BA
Speaking of lateral EQ and Wind loads only...
For shears parallel to the ridge line, the statement is true, assuming equal diaphragms, and equal loads. Just look at the shear diagram - the ridge is at the center of the diagram where the shear is zero. The endwalls should have a double top plate to function as the chord member to make the diaphragm work.
However, for the transverse lateral shear direction, what you say is true. But with the rafter/trusses, coupled with a continuing of the diaphragm plywood to the ridge, with blocking and holes for the venting, it will function to carry shear.
Speaking of the vertical load / deep beam issue only...
I still feel that for this load case, and there are others, it is not necessary to have the diaphrams linked at the ridge if each diaphragm is partially functioning as a deep beam. A portion of the load will flow through the rafters to each diaphragm and to the endwalls.
Mike McCann
MMC Engineering
Now we'll discuss how to fix the holes in a diaphragm.
Mike McCann
MMC Engineering