ASME requirements for outdoor blowdown valves

ASME requirements for outdoor blowdown valves

ASME requirements for outdoor blowdown valves

(OP)
Hello all,

Does anyone know if there are additional requirements from ASME for outdoor valves beyond what is called for under BPV code section I? Basically we have a high pressure water tube steam boiler, 150 psi design, that will be placed outdoors. The boiler will have a roof and a full boiler height enclosure that will extend from the boiler front and house the burner and controls. The gas train, which will be NEMA4, both the quick opening and slow opening blowdown valves and the relief valve will be outside of the enclosure and thus exposed to the elements.

Thanks,

RE: ASME requirements for outdoor blowdown valves


You need to coordinate with the boiler manufacturer, they typically supply the relief valve..  Ensure they spec a valve that is corrosion resistant when exposed to the elements.


But now I am curious.   Money to put in a Div 1 water tube and you really can't extend the raincover over the gas train and blowdown valves? I suppose they make NEMA 4X pressure switches etc. for a gas train that could be used outdoors, but it might not be a standard option..  

Are you are also supporting this "roof" from the boiler itself to save additional cost?  Are there clips for attaching steel, and is the boiler manuf. aware of the loads?

Is your blowdown tank also outdoors??  You'll have to heat trace all that.

just a few thoughts.

Real world knowledge doesn't fall out of the sky on a parachute, but rather is gained in small increments during moments of panic or curiosity.  

RE: ASME requirements for outdoor blowdown valves

*section 1* (typo)

Real world knowledge doesn't fall out of the sky on a parachute, but rather is gained in small increments during moments of panic or curiosity.  

RE: ASME requirements for outdoor blowdown valves

no ASME restrictions.  if in cold climate you will have to insulayte and heat trace  but that's you as owner and the local Inspector/Jurisdiction requirements.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources