(OP)
I'm feeding a 277V/1PH lighting control panel from a 480Y/277V panel that has an available fault of 16k Isc.  The lighting control panel has a rating of 14k AIC at 277V.

Would the available fault current for a single phase load be less than a 3-phase load?

RE: Lighting Control Panels / Relays AIC ratings

A 277 V single-phase panel?  That's a new one.  

Fault current will be reduced by the feeder impedance from the main 480 V panel to your sub-panel.  

But you can't make assumptions - you need to calculate.

There could also be a series rating between the breaker in the main panel and the sub-panel breakers.   

David Castor
www.cvoes.com

RE: Lighting Control Panels / Relays AIC ratings

Further to what David said - the fault will be single phase, so you need to calculate Ø-grd faults.
 

RE: Lighting Control Panels / Relays AIC ratings

Is this really a single phase panel or are you using two phases of the three phase supply?

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Lighting Control Panels / Relays AIC ratings

If you have ONE hot wire and ONE neutral wire going to the LCP from the 480/277V panel, then you need to determine the Isc at 277V {phase to neutral), not 480V. But if you have TWO hot wires and a neutral, then you have to use the 480V value.

 

"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)
  
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources