Smart questions
Smart answers
Smart people
Join Eng-Tips Forums
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login




Remember Me
Forgot Password?
Join Us!

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.
Jobs from Indeed

Link To This Forum!

Partner Button
Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

flat duct transition - poor aspect ratio - estimates on static loss??

BronYrAur (Mechanical) (OP)
28 Jun 11 11:11
I have a low pressure 16"x8" duct that transitions to a 42"x4".  The length of the transition is approx 18".  The 42"x4" duct only runs for 24", and then there is another transition (18"long) back to the original 16"x8"  There is an 8"x4" tap on the 42"x4" piece serving a 100 CFM diffuser.  The remaining 16x8 downstream of the transition delivers a total of 500 CFM.  See attached.  

Any idea how much static is being lost in this fitting?      
walkes (Mechanical)
29 Jun 11 10:23
No idea, but you may get some static regain when it goes back to the original size.  
MechEngNCPE (Mechanical)
29 Jun 11 13:56
Check the ashrae fundamentals for your C value and velocity pressure, do the calc.
lma1 (Mechanical)
29 Jun 11 22:38
The first trnasition is obviously an irregular one. The duct is expanding on the horizontal dimension and at the same time contracting on the vertical dimension. Area- or velocity-wise this may be considered as an unsymmetrical expanding transition fitting. This system might have to be installed that way due to physical constraints or for other practical considerations, it loss is definitely not easy or impossible to estimate!

The designer should strive to design and arrange duct fittings according to some fitting standards or database so the system loss can be estimated.  These are ASHRAE Duct Fitting Database (2009), ASHRAE Fundamentals Handbooks, SMACNA HVAC Systems Duct Design or other technical handbooks or texts.

Notice too the AR (Aspect Ratio) of the transitioned piece is 42:4 or 10.5:1. This is considered bad design. The designer should strive to achieve an AR of ≤ 3:1. In addition to increased surface area, insulation and weight of metal, friction rate and operating cost increase as AR increases.
 
berkshire (Aeronautics)
30 Jun 11 0:07
BronYrAur
That type of fitting would drive me nuts in the dust collection industry, because of the velocity loss in the middle of the transition letting the entrained dust drop out.
 I am presuming you are having to do this to get around or under an obstruction. I think the only thing that might give you some relief would be to make the transitions longer if you have the room to do so.
 In most cases like this you are stuck with what you have got.
   Figure you are going to get velocity and static loss in the center of both transitions. If it bothers you, put a diamond  or lozenge splitter in the center of the transition to keep the velocity up.
B.E.

The good engineer does not need to memorize every formula; he just needs to know where he can find them when he needs them.  Old professor

BronYrAur (Mechanical) (OP)
30 Jun 11 11:07
It was done to make room for some piping.  Fortunately, I'm not the engineer of record, but I wanted to be able to alert them that the static drop may be a problem.  I was hoping to quantify the drop.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close