what is the minimum depth that medium voltage (13,200V) PVC conduits encased in concrete with 3 inches of concrete to the dirt from the conduit? is there a minimum? is the depth to the edge of the concrete or the edge of the conduit?






RE: Minimum depth of medium voltage concrete encased PVC?
RE: Minimum depth of medium voltage concrete encased PVC?
minimum depth for PVC is 18".
You can use rigid to install with only 6" of cover.
Measurement is to top of concrete envelope.