Cable insulation improvement

Cable insulation improvement

Cable insulation improvement

(OP)
With regards to the insulation improvement, Could it be there were moisture present in the air gap of the cable and the moisture was removed during hipot test and that led to an improvement of the insulation level?   
 

RE: Cable insulation improvement

I was present when a low voltage pvc insulated underground cable after installation was tested with 1000 v dc megger and the measured resistance was 0. We isolated the cable receiver end and connected to power source-400 V 50 Hz-for 72 hours. After 72 hours we checked the resistance one more time and this time was almost 1000 Megohms. It seems that the dielectric losses –even very low losses- heated the insulation and evacuated the moisture.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources