catterpillar generator output voltage dropping.
troubleshooting a cat generator, from start voltage output is only 280 volts phase to phase and 110 phase neutral,but after 3 mins running, output voltage drops to 40 volts all phase, and i need 380 volts. what is the problem here? is the voltage regulator 9y8400 damaged? or is it just the wiring?
generator details
catterpillar model sr4b
456kVA
365KW
3 phase
10 wires
connection wye series
generator 480V
excitation 39v
7.5 amp
voltage regulator 9Y8400
generator details
456kVA
365KW
3 phase
10 wires
generator 480V
excitation 39v
7.5 amp
RE: catterpillar generator output voltage dropping.
The answer to this will influence other suggestions, but in the meantime, does the voltage change as the voltage pot on the AVR is changed (in the first three minutes).
Bill
"Why not the best?"
Jimmy Carter
It sounds as if the AVR may be overloading and shutting down.
I am assuming that you haven't put any load on the set yet. If you have, details please.
Monitor the voltage output from the AVR. If the AVR voltage is dropping, the next question is why.
Do you have a Permanent Magnet Generator supplying power to the AVR?
You may have a failing brushless exciter or a failing AVR.
Check the voltage and current out of the AVR. If either are too high it may trigger a shutdown of the AVR.
Bill
"Why not the best?"
Jimmy Carter
Failed diodes are another possibility. With a failed diode the AVR may go to maximum voltage trying to bring the voltage up, and trigger an over-voltage shutdown.
Bill
"Why not the best?"
Jimmy Carter
I think you have a bad regulator.
@waross: i haven't put any load on the set.
Bill pretty asked all the questions I would, answering them would be helpful.
On a safety note, I wouldn't use a battery charger to supply the exciter on an SR4 generator unless you are VERY familiar with what you are doing, which in your case it sounds like you're not. I use a 6 volt lantern battery, if the tail end is good it will build and hold 50-70% of rated voltage. Typical no load rated terminal voltage field volts on that machine usually about 9-14VDC at less than 1 amp.
Could be the AVR but it sounds like it trying and then going out on overexcitation. If you stop it for a while then restart and it does the same thing I'd say it is likely something else. I have seen a few VR3's fail that way but it isn't their common failure mode, they either don't work at all or go full field at start.
The 40 volts you're seeing is pretty typical for the residual level the machine will build at rated speed.
The 9Y8400 (and most VR3's) are nominal 240 sensing, and they are phase rotation sensitive. So make sure the sensing leads are hooked up per the drawing, T1=22, T2=24, T3=20, a lot of people hook them up wrong, and can cause your issues if this is an SE machine.
Mike L.
htt
The LS R448 will work to replace a VR3, especially an SE as long as the correct jumper settings are used.
The VR3 family of AVR's is no longer available from CAT, the VR6 is the normal replacement.
Mike L.