Liquid Seal Vacuum Formation in Tank Gravity Draining Liquid Outlet

Liquid Seal Vacuum Formation in Tank Gravity Draining Liquid Outlet

Liquid Seal Vacuum Formation in Tank Gravity Draining Liquid Outlet

(OP)
I'm installing a drain tank which will normally drain diesel fuel.  The tank can occasionally also receive hydrocarbon gas.  This is vented to a safe area via the tanks vent, but hydrocarbon gas must not be allowed to follow the liquid outlet line i.e. gas blow-by must not occur.  To prevent gas blow-by, the liquid outlet line (which simply gravity drains to another tank) has a simple 'U' tube configuration to act as a liquid seal.

How can I determine if my liquid seal (U tube arrangement) requires a vacuum breaker?  

My concern is that the liquid outlet could form a vacuum in the gravity draining section (downstream of 'U' tube arrangement) and siphon tank liquid content, thereby allowing gas blow-by.  If I concluded that vacuum formation was possible, I would simply install a vent line downstream of the U tube arrangement.  

Thanks in advance.
 

RE: Liquid Seal Vacuum Formation in Tank Gravity Draining Liquid Outlet

The criterion for determining whether you will form a siphon or not is the Froude number. If Fr > 1.0 you will quickly flush the vapor out of the line and initiate a siphon. For Fr < 0.31 the vapor will remain in the pipe and no siphon will form. Between 0.31 and 1.0 the vapor will be gradually moved along the pipe and you may get some instability. To be sure that you do not siphon your U leg seal dry you should either put a vent downstream of the U leg, or design for Fr < 0.31.

There was a detailed discussion of the problem in thread378-289211: Hydraulic Design 101 - Air at Highpoint

Katmar Software - Engineering & Risk Analysis Software
http://katmarsoftware.com

"An undefined problem has an infinite number of solutions"

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources