Roof diaphragm design at different elevations
I have a building that consists of basically two tenants.
One tenant has a sloped roof (1/4" per foot requirement) while the other wants a hip roof with (2.5" per foot). At school, I was taught to take these two tenant spaces as two different buildings. I do have a interior wall that separates the two buildings. This wall is to be the interior shearwall. I will be designing it for the loads from both the buildings (spaces).
I was wondering how would you design the shear transfer from the hip roof to the lower flat (very small slope) if there wasn't any wall present.
RE: Roof diaphragm design at different elevations
It would have to be a continuous diaphragm with a couple of bends in it.
BA
And a lot of blocking...
Mike McCann
MMC Engineering
Motto:  KISS
Motivation:  Don't ask
Are the elevations different where the two diaphragms meet, conceptually?
From the OP's post, yes.
"...the shear transfer from the hip roof to the lower flat..."
Mike McCann
MMC Engineering
Motto:  KISS
If the elevations are different, I would provide a structural frame, or frame supporting a short intermediate wall, to gather the diphragm forces together for transfer to each other, unless the frame could be part of the LFRS.