Concrete around the turn of the 20th century
I am analyzing the retaining wall of a water reservoir in Baltimore County, Maryland that was built in the 1920's and I have no other information regarding the concrete other than it is designated on an old drawing as "Class A" for the wall/footing and "Class B" for the Containment bottom slab.
The only concrete standards I could think of at that time were ASTM, and the early workings of ACI. AASHTO uses letters to designate classes of concrete so I thought maybe they were a carryover from those early mix designs.
-Robert Miller, E.I.T.
KPA Structural Engineers
RE: Concrete around the turn of the 20th century
Kieran
I wish it was in the budget right now. However, if the wall analysis failed with the most reasonably accurate estimate of f'c, we would request for cores to be completed before the additional loads were imposed on the wall.
A previous analysis was completed by a firm, which used f'c = 2500 psi. I have a sneaky suspicion that the design compression strength was higher, not to mention that the curing over 90 years has probably increased quite significantly.
While portland cement concrete does gain strength with age, that strength gain will plateau after the first year or so. One thing that makes concretes of that era gain strength for a longer period of time was the coarseness of the cement grinding. Even though that has occurred over time, I would not consider much beyond about 110 percent of expected design strength, simply because of the variability.
Concrete can lose strength with age, mostly due to environmental factors. Consistent wetting and drying is one action that can cause this.
I can't understand why your company has gone into an evaluation of an aged structure without due consideration for evaluation of the materials, including coring, petrographic examination and strength testing. These items should have been in the budget.
I have some older references in my library at the office. I'll check on Monday.
Ron
Checked a few references I have, the oldest back to 1929, but no mention of "Class" of concrete. In my experience, that terminology often comes from state Departments of Transportation and as you noted, AASHTO, though in that time frame, it was AASHO, not AASHTO. Further, the Bureau of Reclamation drove a lot of standards and terminology in that era.
I would suggest two paper search approaches....
1. Check with the Portland Cement Association (PCA) in Skokie, Illinois. Their reference librarian/archivist might have something.
2. Check with the Maryland DOT to see if their early specifications used that terminology. Also, it is possible that Baltimore had its own building code at that time. Check that.
Good luck...these things are often difficult to chase down, but always a learning experience!
Ron
I also found the attached PDF of concrete info, from about 1900. There is a reference to class, and it may help with starting design figures.
cheers,
Linnea
I recently did some falsework design for an arched bridge rehab in the Boston MA area. The original bridge arches and walls were constructed around the same era. AASHTO recommends the assumption that concrete of that era has a compressive strength of 2,500 PSI. This was inadequate for the anchors I was using, so I requested that the contractor have a testing lab obtain and test a few cores from the walls that the anchors were going into. The test results indicated an average strength of 5,010 PSI with little variation. The point being that the concrete could have a surprisingly good compressive strength that only testing will determine.
Ralph
Structures Consulting
Northeast USA
I agree with that AASHTO recommendation and I know that the concrete has significantly more strength than 2500psi, but we cant core drill so there is not a more precise way to quantify it. I think the thought process (from my superior) is that if the concrete fails in analysis with the best possible assumptions, we can go to gathering core samples. However, if it passes analysis with 2.5ksi, we have a conservative solution.
I just like to have all my I's dotted and T's crossed before I assume anything. You know that old idiom...
There are days when I wake up feeling like the dumbest man on the planet, then there are days when I confirm it.
In the end, I'm leaning towards AASHTO (or AASHO as it was formed in 1914) or the local jurisdiction of the structure. A phone call to the local jurisdiction might have answered it..
http://www.hpcbridgeviews.com/i55/Article3.asp
You might check further...
Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
Common sense, practicality and experience are not allowed...stop it!
Mike McCann
MMC Engineering
Motto: KISS
In your case, did the firm that performed the previous analysis provide any basis for 2500? On the plus side the reservoir is still standing.
I am betting that the environmental factors were a bit harsher on that concrete for your colleagues bascule bridge. Unfortunately for our client, the previous firm's analysis was awful, along with their short report describing their findings. One of many things, they assumed deformed bar at 36 ksi, which was not even manufactured until the 30's.
However, from some of my cross referencing and from some help from some people on eng-tips, 2500 psi seemed to fall in line with old AASHO & ASTM standards for dams/retaining walls with moderate exposure.
I understand the Panama Canal locks were one of the first large modern reinforced concrete structures, and they were 1910-1916 time frames. This problem is only a few years after that.
Also, as we all know, concrete is inherently relatively unpredictable, so until recently (say 30 years or so), admixtures have allowed greater performance and predictable behavior, especially with the greater implementation of post-tensioned nuclear containment buildings in the late 70's/early 80's.
So...my best guess is the time period when post-tensioning of nuclear structures began.