conduit fill usins 3/c calble

conduit fill usins 3/c calble

conduit fill usins 3/c calble

(OP)
NEC states dimensions & percent area of conduit/tubing 1-wire. 2-wire etc. There's personal saying a 3/c conductor is to be used as over 2 wires @ 40% code states 3/c used as 1-wire 53%, problem is I can't put my finger on this Article,please point me in the right direction on this subject. Thank you

RE: conduit fill usins 3/c calble

If you are pulling in one thing, regardless of what's inside the thing, then use the one conductor sizing.  If you are pulling in three things, regardless of what's inside the things use the more than two conductor sizing.  The geometry problem doesn't depend on what's inside the thing you are pulling in, just the size and quantity of the things that you are pulling in.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources