Calculating three phase power

Calculating three phase power

Calculating three phase power

(OP)
How can I calculate the output power from a 3 phase UPS with unbalanced loads?
Load  Voltage(Vrms)R-Y 409.8   Y-B 414.3   B-R 414.1    
Load  Voltage       R-N 237.4   Y-N 238       B-N 239.7    
Load Current(Arms) R   79      Y   27.7    B   41.3     N   68.4    
Our engineer attached a Fluke scope meter to each phase voltage and current and then added them together. This came out at approximately 60kVA. But if you use P=V*I*1.73 for each phase and then sum these results this adds up to 105.6kVA.
Anyone help?

UPS engineer http://www.calibrepower.co.uk

RE: Calculating three phase power

Google "power factor"

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Calculating three phase power

P=V*I*1.73 is for a "balanced" 3 phase power system, that is when I is equal in all three lines and V= V line to line.

For unbalanced system, calculate per phase values and add them up.

For each phase power, the formula is V*I where V is line to neutral or (Vll/1.732).

Rafiq Bulsara
http://www.srengineersct.com

RE: Calculating three phase power

Notice that if you take your 105 kVA and divide by 1.73 you get the engineer's solution.  That's a hint that you mis-applied an equation somewhere.

RE: Calculating three phase power

Probably used the line voltage and not the phase-neutral voltage...?
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: Calculating three phase power

Quote:

Our engineer attached a Fluke scope meter to each phase voltage and current and then added them together. This came out at approximately 60kVA.

How was that connected and measured? Given your numbers, the only way I can get close to 60 kVA is by using the peak instead of RMS L-N voltages.

 SUM( Vln * Il ) = 41.7 kVA

  Vln = line-neutral voltages (Vr-n, etc.)
  Il  = line currents

Using the line to line voltages, the proper formula is

 SUM( Vll * Il )/ 1.73 = 72.3/ 1.73 = 41.6 kVA

  Vll = line to line voltage

which is close enough.

Quote:

But if you use P=V*I*1.73 for each phase and then sum these results

But you don't. That will work for a balanced situation where V is Vll and V and I are the balanced line to line voltage, line current. But then you don't sum them.

RE: Calculating three phase power

(OP)
If I apply Rafiq's calcs I get 35.2kVA.
My post did not state clearly how my engineer took the readings. He attached a Fluke scopemeter to each phase and set the scope to kVA power and then added these results together.

UPS engineer http://www.calibrepower.co.uk

RE: Calculating three phase power

Note:
kW is power.
KVA is apparent power.
You are calculating apparent power, not true power. {rant off}
Yes, I get 35.2 KVA

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Calculating three phase power

(OP)
Bill
Thanks but I realise that and will be applying 0.8pf for this UPS. Didn't want to confuse things any more!

UPS engineer http://www.calibrepower.co.uk

RE: Calculating three phase power

(OP)
Things seem to make a bit more sense now. I think my engineer must have connected his scope phase to phase instead of phase to neutral. 1/1.73*60kVA = 34.7kVA which agrees with our sum of V*I for each phase.

UPS engineer http://www.calibrepower.co.uk

RE: Calculating three phase power

Blondel's theorem - in a system of N electrical conductors, N-1 electrical meter or wattmeter elements, when properly connected, will measure the electrical power or energy taken.

Your system is a 4-wire, so 3-element metering is adequate.

So, 35.2 kVA is the correct answer!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources