ACI 318 specifies maximum spacing between links along the beam span,
however there is no specified value i could find for spacing of legs perpendicular to the span,what do you normally use and based on what?
Regards
ACI 318 specifies maximum spacing between links along the beam span,
however there is no specified value i could find for spacing of legs perpendicular to the span,what do you normally use and based on what?
Regards






RE: Beam Links Spacing
normally this is only an issue if your beam is much wider than its depth or if its primary source of load is axial. Can you give a bit more information on your particular situation?
RE: Beam Links Spacing
This is based on Eurocodes and the relative National Annexes and is given as st,max
RE: Beam Links Spacing
Any tension bar cannot be more than 150m from a vertical leg of a link perpendicular to the span.
Similar provisions exist in EC2.
RE: Beam Links Spacing
I normally provide one keep the spacing perpendicular to span around 300 mm as common practice but could not find any reference in ACI 318
RE: Beam Links Spacing
If I understood your post you mean that for a 40cm wide beam you would need at least an enclosing link and an inner link .
I believe the stmax=0.75d #9.2.2 EN1992.01.01 refers to the maximum distance of vertical links in the beam's width and not along its length.