(OP)
I am designing a chute spillway.
I was thinking of prescribing the concrete as C30/37 but I am having second thoughts of  prescribing the concrete as C35/45

The environment is cyclic wet and dry. Hence according to Eurocode it is XC4 class designation.

The design working life of the structure is 100 years.
However the member has a slab geometry, special quality control of thge concrete production will be ensured and there will be a composition demanding low permeability e.t.c
 

RE: SPILLWAY CONCRETE QUALITY C30/37 or C35/45

I would opt for at least 40 MPa concrete, maybe more, for a spillway.  Surface erosion can be decreased with a higher strength concrete.  I would consider steel fibre concrete to increase toughness and abrasion resistance.

RE: SPILLWAY CONCRETE QUALITY C30/37 or C35/45

Personally I would go with the higher strength concrete as it is a small price to pay for a bit more durability.

The only real problem with the higher strength (as well as the small additional cost) is the additional heat created which may have shrinkage implications for a large mass of concrete.

RE: SPILLWAY CONCRETE QUALITY C30/37 or C35/45

(OP)
The shrinkage is treated as temperature fall.
Replacing in Eurocode's formula fcm=38mpa for C30/37 gives a Temperature fall of -25.17C
Replacing in Eurocode's formula fcm=43mpa for C35/45 gives a Temperature fall of -25.37C
The climate study revealed an average humudity of 79.29% actulaay the lowest value in August,..I am lucky because with such humidity shrinkage is kept relative low.
Calculation wise things will not change..alot since modulus og elesticity for C30/37 is 33GPA and for C35/35 is 34GPA
Only spice and anchorage lengths are reduced with higher concrete.

  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources