We have a parking garage that is constructed of precast concrete double tees that are supported by precast beams and columns.  A number of joints between the double tees are leaking and must be repaired.  There is a 3" traffic topping.

One repair method we want to avoid is to chip away the 3" concrete topping and repair the joint, then pour new topping.  We don't like this idea because there are a large number of leaks to repair - this could be quite expensive.

Is there a good way to repair the joints from below?  Or a more economical approach from the top side?

Thanks

RE: Parking Garage Repair

Is there enough capacity in the system to apply a mastic sealant to the leaks, then a 2" thick Asphalt concrete overlay?   

Mike McCann
MMC Engineering
Motto:  KISS
Motivation:  Don't ask

RE: Parking Garage Repair

Some kind of injection??

RE: Parking Garage Repair

If leaking only between the joints, cut out a 1/2" joint, use etafoam rod and a good polyurethane caulking.

Dik

RE: Parking Garage Repair

Heh - I just got back from looking at the same kind of garage - with leaks as you describe.

Generally speaking, the leaks can come from a number of sources.

1.  Joint failure in construction joints in the topping slab.
2.  Joint failure in expansion joints.
3.  Degredation of the concrete along the joints (chloride attack on the concrete matrix will create a more "powdery" concrete that is more porous - i.e. leaking without cracks.  This is evidenced by weathered, granular-like surfaces near the joints.
4.  Micro cracking in the concrete away from joints.
5.  Leaking along perimeter walls, edges, where joint sealants have failed.
6.  Leaking around drains or trench drains where the concrete-to-drain seal is bad.

All of the above must be combined with a failure of the waterproof membrane below the topping slab.  The problem with membranes such as this is that you NEVER know exactly where the membrane leak is.  It isn't necessarily right at the joints that have failed.

The only methods to respond to this (in ascending order of cost and effectiveness:

Option 1 (lowest cost and effectiveness)
1.  Grind out all joints and replace new sealant.
2.  Re-build damaged joint edges with patching mortar where necessary.
3.  Replace and Re-install new expansion joints.
4.  Cover with a concrete water resistant sealer.
5.  Don't put chlorides on the concrete in winter.
6.  Maintain the joints.

Option 2 (better)
1.  Do all of Option 1 above
2.  Instead of water resistant sealer, provide a traffic bearing waterproof membrane (see Neogard, Carlisle, or Euclid products.)
3.  Don't put chlorides on the concrete in winter.
4.  Maintain the joints.

Option 3 (best)
1.  Remove the topping.
2.  Remove the membrane and replace with a new membrane.
3.  Replace the topping
4.  Provide good joint details
5.  Provide water resitant (breathable) sealant.
6.  Don't put chlorides on the concrete in winter.
7.  Maintain the joints.

I'm sure there are other Options out there - these just come to mind right now.

 

RE: Parking Garage Repair

Good summary, JAE.  The only thing is, you assumed there was a membrane in ugandabob's garage, which may not be the case.

ugandabob...forget stopping water by working on the wrong side (from below).  You will be wasting your time and money.

RE: Parking Garage Repair

hokie66 - you are right.  I'm not even sure if the garage I looked at has a membrane or some tar paper.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources