what's the distance between pole support made frome steel(I-beam) and a sprinkler?
I found in NFPA 13 distances between Suspended or Floor-Mounted obstruction but not pole support that are mounted in the floor and in contacte with the roof.
I found in NFPA 13 distances between Suspended or Floor-Mounted obstruction but not pole support that are mounted in the floor and in contacte with the roof.





RE: distance between pole support and sprinklers
If that is the case, see NFPA 13 2007 Figure 8.6.5.2.1.3. This is called the "3 times rule". Space your sprinkler 3 times the largest dimension of the column away from it's edge, up to 24".
RE: distance between pole support and sprinklers
RE: distance between pole support and sprinklers
You didn't draw the size of the column.
If the column is say 200 mm by 300 mm, then taking the largest dimension that is 3x300= 900 mm. However, the max. required is 610 mm, so put the sprinkler at least 610 mm away.