Hi All,

I have a feeder supplied from variable frequency drive (50 -200Hz). This feeder needs a overcurrent protection. But digital relays are not able to provide protection for varialbe frequencies (50-200)Hz.

Is electro-mechanical relay suitable for variable frequencies ? Or what other options to protect this feeder ?


 

RE: Over current relay for 50-200hz feeder

After a quick search on the internet I found this:
http://relays.tycoelectronics.com/datasheets/wd_ds.pdf

Take a look at the WD5051.  "WD5051 AC current sensing relays provide current monitoring and protection in AC systems from 50 to 400 Hz."

RE: Over current relay for 50-200hz feeder

Hang on a minute.  A VFD running PWM on a x kHz carrier to produce a 200Hz input to a motor is putting out x kHz, not 200Hz.  Why not just use the built in functions of the drive?

RE: Over current relay for 50-200hz feeder

I agree with davidbeach. The nature of a VFD's output could affect protection relays proper operation adversely.

Unless the VFD manufacturer has tested the operation of their product with a specific relay (or vice versa), you can't be certain that the two will play well together.

What leads you to believe that the VFD's built in protection is insufficient for your application?

RE: Over current relay for 50-200hz feeder

(OP)
Hi PHovanian / Davidbeach,

Thank you for valueable inputs. I was in same line with you guys to use the in built protection of VFD but client was insisting to put extra protection.

However, once you get 200Hz in your feeder,What is a problem to use WD5051 AC current sensing relays as suggested by JG2828.

 

RE: Over current relay for 50-200hz feeder

Because you don't have 200Hz, you have somewhere in the 5-10kHz range.  There is almost nothing other than the VFD that is producing the mess and the motor it is running that can make heads or tails of the noise and hash on the line.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources