Dear everybody,
Would you like to explain me about Tangen Delta testing for motor?
What is purpose?
Is that important for motor?
Thank you for your response
Regards
Jono
Would you like to explain me about Tangen Delta testing for motor?
What is purpose?
Is that important for motor?
Thank you for your response
Regards
Jono





RE: TANGEN DELTA Testing for motor
It provides some indication of moisture, contamination, or insulation defects.
Also the powr factor can be measured at two voltages and a tip-up can be computed which indicates resistive losses increasing more than linearly with voltage. Possible indication of voids, but present to some extent on most motors.
Capacitance is usually determined in conjunction with the test, and phase-to-phase tests may be conducted in addition to phase to ground if neutral connection is accessible.
I don't believe this is used very often as a routine field test. The equipment is somewhat expensive.
It has been suggested in some Doble papers that this test is particularly useful as a quality-control test of windings prior to insulation. Note that after coil installation the test is somewhat limited for high-voltage motors with corona suppression system because the non-linear leakage current (increase faster than voltage) in grading/gradient treatment at slot exit cannot be effectively guarded out after installation.
RE: TANGEN DELTA Testing for motor
So, where can I get literature/source about that?
RE: TANGEN DELTA Testing for motor
http://www.usbr.gov/power/data/fist/fist3~1/3~1_8.htm
RE: TANGEN DELTA Testing for motor
If the supplier of your equipment is Doble, they will provide you with all the info you need.
RE: TANGEN DELTA Testing for motor
http://www.wapa.gov/rm/psmmpage.htm