concrete slump for SOG

concrete slump for SOG

concrete slump for SOG

(OP)
Wondering what you ladies and gents are specifying these days for slump. We currently call out for 4" max slump for all concrete, except 3" for SOG. Its been in our general notes for a long time and I honestly don't know where it came from. Never had a question, comment, problem or concern, but a peer reviewer (SE) that I respect said these are "very low slump numbers".

To avoid tangents and long theoretical concrete mix discussions, I know the answer could be "it depends on ____", especially the mix design. But just looking for your typical slump range for the following that you may have on your general notes for average projects. We are in Florida, USA if that helps.

Footings-
SOG-
Tilt-Panels-
Concrete on elevated slab-on-deck (composite slab)-
 

RE: concrete slump for SOG

a2...it depends on how you get the slump!  If the slump is obtained with a plasticizer, then 5" +/- 1" is fine.  If the slump comes from water addition and a compromise to the w/c ratio, then keep the slump low.

In short, it depends on the mix design.

RE: concrete slump for SOG

(OP)
Dangit Ron! I knew you were going to respond just like that :)

In short, what about modifying our general notes allowing the mix design to add plasticizers and allow an increase in the slump, submit mix design for review?

RE: concrete slump for SOG

EXACTLY! Specify a slump of 4" (under ASTM C94, that gives a +/- of 1".  The state that if greater slump is required for placement, then plasticizers (high-range water reducing admixtures) must be used.  Submit mix design for either or review.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources