aci 301-05 vs 301-10
aci 301-05 vs 301-10
(OP)
301-05 states
1.6.3 Testing responsibilities of Contractor
1.6.3.2.d Provide and maintain adequate facilities on
the project site for safe storage and initial curing of concrete
test specimens as required by ASTM C 31/C 31M for the
sole use of the testing agency.
Obviously I don't have 301-10 yet. I've heard that the responsibility for the initial curing environment has been shifted to the testing labs in the 301-10.
Any truth to this?
1.6.3 Testing responsibilities of Contractor
1.6.3.2.d Provide and maintain adequate facilities on
the project site for safe storage and initial curing of concrete
test specimens as required by ASTM C 31/C 31M for the
sole use of the testing agency.
Obviously I don't have 301-10 yet. I've heard that the responsibility for the initial curing environment has been shifted to the testing labs in the 301-10.
Any truth to this?






RE: aci 301-05 vs 301-10
RE: aci 301-05 vs 301-10
RE: aci 301-05 vs 301-10
I don't know if 11 is available yet - I'd have to check the ACI website. I could look up the 08 tomorrow if you need me to.
RE: aci 301-05 vs 301-10
boffintech is talking 301, not 318.
To the question, you heard correctly, the contractor is required to provide a location with power rather than the curing box or otherwise.
If you are an ACI member, the chairman of the 301-10 committee has a number of articles in CI highlighting the changes.
http:/
Daniel
RE: aci 301-05 vs 301-10