Are control joint spacing requirements the same for interior walls as for exterior walls?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: CMU Control Joints
In my area, we typically see 24 ft. exterior spacing and 32 ft to 36 ft interior.
RE: CMU Control Joints
NCMA Teks