cosphi problem

cosphi problem

cosphi problem

(OP)
While turbine is running, cosphi is decreasing from 0,95 to 0.35-0.40. Current is increasing from 30 A to 60 A. Voltage is decreasing from 10.800 to 10.000 V. Alternator is 50 Hz.Also, alternator NDE and DE side vibrations are quiet high that is about 6 mm/s on both sides and turbine gives alarm. Vibrations are measured with external device and it shows 6 mm/s too. What might be problem? this happenned suddenly.

RE: cosphi problem

Sounds like an AVR problem, or more likely a correctly-functioning AVR which has been placed in the wrong operating mode. Does the PF go leading (VAr importing) or lagging (VAr exporting) when the voltage drops?
 
 
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: cosphi problem

(OP)
actually we couldnt see it. We have no experience on these. WE asked to some companies about problem. They say alternator rotor might have problem such as short circuit. Is it possible?

RE: cosphi problem

A rotor short is the first thing I thought of.  Do you have any type of rotor ground fault detection equipment?

rmw

RE: cosphi problem

(OP)
no we dont have. We must have service for this.  

RE: cosphi problem

Where are you in the world and what make (brand) of generator is it?

rmw

RE: cosphi problem

(OP)
in Turkey. It is AEG kanis 1,6 MW alternator.  

RE: cosphi problem

(OP)
a service company measured poles, checked bearings and coils. There isnt any problem. However, high vibration on alternator bearings still existing.We suspect AVR systems.Might it be?  

RE: cosphi problem

It's still possible that you have a rotor fault which only becomes active when the rotor is spinning at rated speed, which can be tricky to pinpoint.

Does the AVR have different modes, such as voltage control, power factor control, constant reactive power, etc? What mode is selected? Do you understand how each mode will interact with a larger system?
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: cosphi problem

Measure vibrations with an external, hand held device, to confirm the vibrations given by the control system.

Electrical faults can be read by vibration systems as high vibrations (induced noise)

If the vibrations measured by the hand held equipment (like IRD or Bently Nevada):

1. matches the control system: there might be a problem in the generator field (rotor).

2. are different (and very low): there might be an electrical problem in the exciter.


Hope this helps, tell us how you fared.  

saludos.
a.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources