(OP)
I have heard that service request 15 will allow me to log the last PLC I/O fault into a register. I am using Proficy 6.0 Does anyone have any suggestions for implementing service request 15? Thanks.

RE: I/O Fault table

Run Service Request 15 when %SA3 comes high, that is any Application Fault, or %SA23, an I/O module fault. Search PME's online help for more "System Variables" for more fault bits.
 

RE: I/O Fault table

(OP)
Thanks. This is a GE Fanuc 90-70 PLC with genius blocks. Thanks for any help from anyone.  