Kitchen Equipment, heat gain

Kitchen Equipment, heat gain

Kitchen Equipment, heat gain

(OP)
Does anyone have a good resource (ie. website or excel file etc) that contains latent & sensible heat gain values for kitchen equipment? Both hooded & non hooded...With a usage factor.

Thanks!

 

RE: Kitchen Equipment, heat gain

2009 ASHRAE Handbook - Fundamentals, Chapter 18, tables 5A and 5B.

RE: Kitchen Equipment, heat gain

ASHRAE Fundamentals 2009 18.9 Table 5-E

knowledge is power

RE: Kitchen Equipment, heat gain

*A-E

knowledge is power

RE: Kitchen Equipment, heat gain

(OP)
Ok, I actually have that on a CD.


Im looking at table 5B. What is you suggestion on how to input this into my load calculation software.

My software just asks me for a latent & sensible input for additional equipment. Lets take the cheesemelter for example.

Cheesemelter:

Rated: 12,300 Btuh
Standby: 11,900 Btuh
Sensible Radiant: 4,600 Btuh
Usage Factor: .97
Radiation factor: 0.39

So if I have two boxes in my load calculation software (sensible,latent) what would you suggest punching in?

Sensible:________
Latent: _____

RE: Kitchen Equipment, heat gain

Sensible = Sensible Radiant (since most sensible heat will exhaust up the hood).

Latent = (mass of cheese (slugs) * aceleration)
            (_______________________________) x
            (              gravity                    )    


         (cheese melt factor x usage factor / radiation factor)

which is usually negligable, so I tend not to calculate.

knowledge is power

RE: Kitchen Equipment, heat gain

(OP)
Ok, so for the sensible in this case it would be 4,600 sensible because there is a hood.

With NO hood it would be 11,900 * usage factor?

RE: Kitchen Equipment, heat gain

One point I would like to ask about:
when we say unhooded equipment we have two cases:
1- the equipment itself is not directly under a hood  but there is a hood in the same space
2- there is no hood at all in the same space

ASHRAE tables provide very good help but you have to read the ASHRAE book too not only tables.

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources