star-delta start up
star-delta start up
Iv got a star-delta start up in place,however the motor isn't starting in star but is kicking in at full speed on delta. what could cause this?
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
RE: star-delta start up
If we learn from our mistakes I'm getting a great education!
"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
thread238-298383: star delta starter problems
If this is true, the current should be about 2 x the rated current of the motor, then the problem is probably that you are trying to start a load that requires a high starting torque and the star/delta starter is not correct for this application.
What is the load that you are trying to start?
Best regards,
Mark.
Mark Empson
Advanced Motor Control Ltd