Is there a standrad design method for slab on grade? I need to determine if a 5" SOG will be able to hold a 6"x12' tall non-load bearing cmu wall (all new construction).

RE: SOG Design

(OP)
Also: Is it necessary to brace all non-loadbearing partition walls at the top? There are some 4"/6" toilet partitions which are not full height. How do I, or do I need to brace them at the top and dowel them into the floor below?

RE: SOG Design

Look at ACI 301 and aCI 360.  

For what it's worth, our typical detail for non-load bearing CMU partitions has a thickened slab under it.  

Yes, the wall needs to be braced at the top.  I usually provide a bond beam at the top with angles connecting the bond beam to the structure above.  The vertical legs gets slotted holes to allow the structure above to deflect without loading the wall.   

RE: SOG Design

IBC requires interior partitions greater than 6 feet tall be designed for 5 psf "wind".  Partitions should be braced such that if a person leans or falls against them, they do not collapse or displace.  If they have ADA handrails or such, design for these loads as well.

If the walls can work with these and other required loads without being braced, then you are OK without bracing.

RE: SOG Design

That 5psf is actually a LL, not a wind load.   

RE: SOG Design

Agree with Lion, with CMU partition walls we always use thickened slab footings. For cantilevered CMU walls where you cannot brace the top like Lion explained, such as with a toilet partition, you have to design vertical reinforcing in grouted cells for 5psf lateral which with something like 4" CMU can be harder than you would think. You may be able to tie perp. walls together and use a bond type scheme as well...

If you have to support the walls on plain concrete slabs there are some good design methods in Army/Navy publications, I can look it up later if you cannot easily find this online.

RE: SOG Design

Depending on the seismic region, the width of the block, and the level of grouting, seismic on the wall may govern over the 5 psf figure.  

Remember that figure is only the minimum to use.

Mike McCann
MMC Engineering
Motto:  KISS
Motivation:  Don't ask

RE: SOG Design

Good point Mike.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources