TRI CLAMP sanitary fittings in ss rigid electric conduit
TRI CLAMP sanitary fittings in ss rigid electric conduit
(OP)
Hello,
is a tri clamp sanitary fittings allowed in a rigid ss electric conduit for an industrial food processing machine? I don't find nothing regarding this in the NEC (NFPA 70) codes regulations.
is a tri clamp sanitary fittings allowed in a rigid ss electric conduit for an industrial food processing machine? I don't find nothing regarding this in the NEC (NFPA 70) codes regulations.






RE: TRI CLAMP sanitary fittings in ss rigid electric conduit
Sanitary fittings are not for electrical conduit.
______________________________________________________________________________
This is normally the space where people post something insightful.
RE: TRI CLAMP sanitary fittings in ss rigid electric conduit
344.6 Listing Requirements. RMC, factory elbows and couplings, and associated fittings shall be listed.