Shear wall to sole plate connection distress

Shear wall to sole plate connection distress

Shear wall to sole plate connection distress

(OP)
I have a project that has experienced deterioration of the lower 2-4 " of the OSB wall sheathing. The bldg is framed w lt gage metal studs acting w the OSB as a shear wall.The building is 4 Stories.  Exterior is clad with a brick veneer.    Questions are as follows. how critical is the attachment if the OSB along its bottom edge as it contributes to the shear wall strength? Is there a way to calculate the lost capacity of the panel? Can it be retrofit from the interior by adding stiffiners between studs? If not, what is the minimum height to which new sheathing should be replaced? Any comments or suggestions would be appreciated.

RE: Shear wall to sole plate connection distress

What caused the deterioration?

RE: Shear wall to sole plate connection distress

The attachment is critical.  How to guess what it is worth now - probably not much.  

What kind of deterioration??  Pull off the drywall, install new APA rated sheathing, re-drywall.  OR go over drywall with new OSB and re-drywall.

Fixing all the trim, doors and windows will be a joy!!

 

RE: Shear wall to sole plate connection distress

(OP)
Great idea to sheath from the inside. water damaged caused the deterioration.  source has been corrected.

RE: Shear wall to sole plate connection distress

Assumed water intrusion was the cause.  Agree with Mike.  Possibility of interior approach to repair; however, you say the source has been corrected...are you sure?  Brick veneer needs a very good flashing system that bleeds to the outside.  If the "repair" was to create a "barrier" wall...it won't work.

RE: Shear wall to sole plate connection distress

Like Mike stated, the connection is critical.  I agree with adding sheathing on the interior face of the wall.  I would add full depth blocking between the studs at some elevation and attach the new sheathing to it.     

Jason A. Partain, P.E.
www.myconstructionfinds.blogspot.com
 

RE: Shear wall to sole plate connection distress

With interior partition and/or bearing walls framing into the exterior walls where the problem occured, I would be mindful of the location of any holddowns, making sure the new sheathing is continuous between them, or additional holddowns will have to be added.   

Mike McCann
MMC Engineering
Motto:  KISS
Motivation:  Don't ask

RE: Shear wall to sole plate connection distress

Agree with Ron.  If the flashing is subpar, the deterioration will repeat.

RE: Shear wall to sole plate connection distress

This is the one case where flashing is both legal and mandatory, so make sure it is done correctly.   

Mike McCann
MMC Engineering
Motto:  KISS
Motivation:  Don't ask

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources