vent pipe for underground house
I designed and am building an underground (dirt on the roof) house. The south wall is exposed like a walk out basement,the roof is covered with 18" of soil as well as the entire back wall.Most of the side walls are covered also.
I installed a 4" PVC pipe under the floor slab. and it comes up to the floor level at the 2 back corners of the house where I will put 4" diameter grates level with the floor slab. The 4": pipe goes out thru the front foundation wall about 3 ft below grade. Grade slopes away from the house. My plan is to dig a 3ft trench for about 100' away from the house and extend the 4" pipe in the trench out to where it will daylight at an exist bank.
Here I will build a concrete box around it and cover with screening to keep bugs,snakes,etc. from entering.The idea of the pipe is that it will provide ventilation and in summer when its 90+ degrees and 90% humididty, as the air moves up thru the pipe, the humidity will condense on the pipe walls and run out the end so cooler dryer air enters the house because the pipe is surrounded by 55degree soil. In the winter this would heat the air some justthe opposite effect if its say 32 degress outside of colder. At least this is the premise that Ive read.
The question is what mechanism pulls the air up thru the pipe? Is it some natural movement of air inside the house? Or must I have a tiney fan that has a small vent hole in the top of the front concrete wall to get air flow thru the pipe?
Anyone have any experience with such a Vent pipe?
RE: vent pipe for underground house
For the air to move on its own it will have to be less dense than the air in the house: your cool air will be more dense, especially after condensing out the moisture.
Where does the air already in the house go?
If you are condensing moisture on the wall of the pipe it very likely will mildew.
Spend the money on your (ground source) heat pump if you want to take advantage of geothermal exchange.
How about putting a U-trap in your pipes, calling them floor drains, and installing a nice ground-source heat pump?
To answer your question, air would be drawn into your pipes as warmed air left the house through roof vents.
Mike Halloran
Pembroke Pines, FL, USA
Any ideas on how big a fan I need just to get "some" small movement of air into the house?
You may be right this could be a useless pipe dream. I sure hope it at least provides ventilation. I am a Civil/structural engineer so I really dont know much about this issue other than all the references Ive read on underground houses.
Regarding the mold/mildew problem, if the pipe is on a continuous slope to it's daylighted end, then no water should accumulate in the pipe. it should run out the end. Being that the pipe is smooth wall PVC, even if the insides are damp sometimes, could mold/mildew actually grow if there is no "food" source? Wouldnt the PVC material preclude mold growth as PVC is not a food source ?
Do you think that a hundred feet of pipe may not be enough to let hotandhumid air drop out its water while flowing up the pipe?
I must look up ground source heat pump as I dont know how they work. I assume you need electricity for that system?
THanks for your comments and anymore you can add. I appreciate your responses.
"even if the insides are damp sometimes, could mold/mildew actually grow if there is no "food" source"
I would agree with others that typical passive moisture removal systems like this, and even some active ones, are Legionella factories waiting to happen. Warm, moist, air is the perfect growing environment for a host of organisms. And, there are plenty of food sources in the air, notably, you, or more precisely, the dead skin, etc., that you slough off every minute of every day.
TTFN
Chinese prisoner wins Nobel Peace Prize
Ted
The main article i read was about what they called an "umbrella house" it was dome shaped and had these passive heat exchange pipes as they called them. The inside temp of this umbrella house was very stable and no mold or mildew problems. You can Google it and see the aricle. Its pretty short.
Are you thinking that just the incoming air would have enough food source within it to grow the mold/mildew?
The new densglass drywall's claim to fame is because it has no paper mold and mildew wont grow on it. wouldnt it be the same for the pipe?
I too have the same concern about mold/mildew in the pipe but Im just not sure.
I like the idea of the pipe vent but I'm not sure about it either.
I would be nice when the place is locked up for say a month in the summer, to leave a very tiney fan running and have this vent system work to keep humidity levels down in the house while it is vacant.
The mold and mildew problem is a real concern in your 90% humidity area. UG houses were a fad in Minnesota 30-35 years ago, and they just didn't pan out. Houses need to breathe well in such climates.
Good luck on the project.
I was in the building once.
It was uncomfortably humid, not nearly cool enough, and was clearly breeding its own hordes of mosquitoes. ... inside. ... and it stank of mildew.
Mike Halloran
Mike
You'll pull fresh air into the house and slightly pressurize the air inside of the house. The latter will prevent hot/cold air from coming in through an open doorway when people enter/exit.
The house is a simple rectangle with a single pitch shed type roof. It has windows all along the south side and 1 small window on the east and west side where the side fill allow enough room, so these little winodws are about 6 ft from the south wall.From there back,(about 16 ft) there are no more windows.
This is located in northern,Pa. so most of the time hot and humid weather is not a concern,however in summer as you know hot and humid weather can and does occur. The house will be heated with a small effeicnet woodburning stove and i will put in a few baseboard electric heaters that I may want to turn on once in a while to take the chill off when its just slightly chilly.
Thats it as far as heat. I will have a dehumidifier just in case I need it in spring and summer.
Do you know anyone who had a passive underground pipe vent system like this that worked ok and didnt grow mold?
Fresh air intake for the woodstove? If you've had wood heat before, you already know how it dessicates the house in the winter. The ultra-dry air excaberates the effect of any mold spores present in the air. (EG: bronchitis, respiratory irritation, etc)
Why add both electric baseboard and wood stove? The house should be well sealed except for the controlled vents and require only a small heat source. Hedging your bets seems to indicate you don't trust the design. Might as well add an air conditioner, just in case.
Check out temp controlled RV vent fans. They run on DC power.
Ted
What is Engineering anyway: FAQ1088-1484: In layman terms, what is "engineering"?
TTFN
I figure its cheap to put a few baseboard electric heaters a few places just for convenience.
The vent pipe would sereve as air sourcefor stove also.
I guess the big questions are still
.how big a hole do I drill/cut thru the top of the front wall for the chimney effect to let hotter air out when air is coming in thru underground vent pipe
.If i decide to put tiney fan at that hole in wall how tiney a fan do i need to bring in enough ventilation thru the vent pipe
.is a hundred feet of underground 4 inch pipe enough to get the condensation effect in action for hot humid air coming thru pipe.
This I guess is a thermodynamics questions combined with gas flow-if velocity of air is too fast thru pipe then maybe it doesnt have time to do the heat exchange thing.
.will mold grow inside pipe even though it is on a steep pitch to daylight so no standing water can occur.
http://h
You don't want to pull too much air or you may backdraft your stove and draw smoke into the house.
Ted
http:/
They use 8" and 15" pipe. Buried 5-6ft to get into the constant temperature ground and below the frost line.
Ted
In the (now) 100+ year old farmhouse that I grew up in, we had a "cooler" built into the north wall of the house. Essentially a cupboard with slatted shelves, and two vents (upper and lower) through the north wall. Stored vegetables and certain adult libations there, more as an overflow for the fridge. It sorta worked. It also tended to be a source of drafts whenever the north winds blew (winter).
We lived in a brick house built in the 30's and couldn't understand why the dishes in one kitchen cabinet were always cold. The cabinet had been built over a cooler that had top and bottom vents through the wall.
redun, a larger pipe would give more surface for heat exchange and lower air velocity to allow more condensate to drop out in the pipe. Yes,the slope away from the house would carry the condensate away. I thought the numbers used in the link would be of interest; moisture condensed and temperature rise or fall. I didn't find mention of length of pipe for their figures. Curious.
Good luck. Let us know how it works out.
Ted
Depending on your total environmental envelope you could easily add a small high efficiency (high SEER) heat pump type air conditioner. You effectively have a super insulated house so air quality will be a problem.
I haven't run out any details the units from BPE might be the best approach.
http://www.bpequip.com/residential.dws
Addenda:
I ended up with my shop being super insulated and quickly learned that air quality was problem everytime I did anything in the shop. I had to put in an air exchange system. I took the penalty of a small in loss of efficiency as my current heating and cooling system are too big for the reuired load.
Fresh air ~10 cfm/person assume 6 people max capacity = 60 CFM
100 ft 4" pvc pipe gives .27 inches water head loss
5 elbows add gives .135 inches water head loss
Cap and screen gives .135 inches water head loss
Total loss 0.64 inches of water
so your pump must be a 60 CFM at .64 inches of water head
60 CFM in a 4 inch pipe give 688 ft/min pipe velocity. This velocity may be too high to condense water out of the make up air. Consider a 6" pipe, 60 CFM will be 306 ft/min pipe velocity at .08 inches of water head. A test would be easly constructed and evaluated for both temp and humidity.
It seems that there is some reasonable doubt that the ducting systems can be kept mouldfree.
If you rephrase your problem it could read as:
How to minimize installation, operation/maintenance and consumption cost for a 'green' temperature and energy system controlling humidity and temperature in an underground house. If possible by utilizing earth warmth and natural ventilation by ducts (PVC).
Summary and comments on 'known facts'
1. PVC pipelines seems smooth, but even good quality plastics have pores and will present growth possibillities for milddew and bacteria. Aging process of plastics, although slow. Lifetime xx years?
2. Known problem with superinsulated houses: air quality will often be low, as air circulation often is set/regulated several times lower (up til 1:5 or 1:10?) lower than by older constructions. Air circulation from inside out and vv. should be controllable and amount at a level upholding quality. Higher underground necessary than above?
3. With humidity/temperature higher outside than inside, air intake will give condensate on colder surfaces.
4. Walls, roof (and ceiling), and inner walls to be constructed to give protection against humidity coming from surrounding earth penetrating to inside of house. (Else excess and constant drying and ventilation necessary.)
5. Inner surfaces of house isolated or protected against humid air from outside to give condensation on colder inside surfaces. (Else air intake more needed to be dried)
6. A wood burning oven construction as often used in Scandinavia:
A pipeline for air intake from outside of house led directly into oven to avoid draft in house, diameter depending on capacity of oven, normally used about 2". Might be buried in floor.
Pipe for smoke and hot air from oven (smokestack), even one meter (metal) free will give as much as 1 kw extra. Might also construct larger heat magazine (brick, clay Mexican construction, 'kakeloven' or other).
The direct air intake construction will not necessarily need extra drafting from room/house (possible excemption when lightening with open door or room vent) if smoke-pipesize and intake is dimensioned sufficient to oven capacity. One can however regulate air intake into the house by opening door oven vent intake and open vents (normally above windows)
7. Modern electrical panel (ovens) have metal heating magazines of some size and very narrowbanded thermostats (0,3deg C) and can be adjusted at low cost to give low-cost 'warm-air curtains' in front of (glassed) cooling surfaces.
8. The house entrance(s)should be built with an airlock (closed smaller room with extra door to minimize uncontrolled air exchange.
9. Additional to 'main controlled' air intake the house should have some smaller (2-4") manually adjustable / controllable / shutable / easily cleanable (with chlorid water) vents. About 8 feet above floor, over windows?
And finally comes the key questions:
With the house construction as described, the earth and hence the house temperature would be relatively stable, somewhat cooler in the winter than summer.
If we now add 'living in the house' as some extra heating sources (warmwater, electrical equipment, lights, cooking, people) and some air exchange what will the temeprature be over the day7night and seasons? (This can be calculated!)
Will the living be sufficient for a stable comfortable temperature?
The answer is no.
At a guess mostly heating will be necessary. In spring, summer and early early autumn perhaps partly during day by sun intake, and shading when to much heat?
If extra heat needed: as in winter.
In winter heating could be done by burning wood, electrically by air/air heat exchanger (as cheapest for circulating inside air wich will also give higher conmfort circulation alone about 10W) and heating (100-300W) at air temperature about 8 deg C or higher). Figures approximately for a 250m3 house.
Cooling in summer at a guess mostly/all by surrounding earth?
The main problem then is mainly to control humidity in the air intake in summer.
This problem might possibly be solved by a 'technical room' where the air/air heat exchanger is placed, where straight cleanable/accessible ducts are placed, and air intake into the room perhaps passes 'some suitable cool metal plates' to remove excess humidity in summer above what is condenced in pipeline (or last part of pipeline stainless).
Note: air amount balance necessary to give heat to heat exchanger is not calculated! Duct size and need of forced air not calculated! (Can be calculated!)
In winter the technical room will have air temerature about earth temerature.
The technical room to be isolated from the living area, and will in summer work as dried air intake reservoir. (Possible to control air temperature by having several pipes to different levels (shorter cooling length, throttable vents? Somewhat forced intake from technical room to house? Sunpanel/battery powered fan)?
'Normal' visible draining from ducts in the technical room into small reservoir (cleanable)and normal draining system out together with gray water from the house.
In winter (low humidity) air intake should be directly from outside, throtteled and controlled to balance comfort and running heating sources: wood, electrical or air to air or combinations as suitable.
Sorry about the lengthy comments, but I got really carried away by the concept!
Good luck!
Further, I can't imagine by any stretch, that 40F is comfortable inside. Maybe I'm a bit jaded since I live in the southern US, but even 65F inside is uncomfortable to me.
I have seen very few of these systems work for the long term.
gerhardl, Thanks for your long list of thoughts and issues for consideration.
I must try and digest all the info. posted here so far. I must do some calculations of my own and see what I come up with and post an update. In the meantime ,any more thoughts are Welcome
The transition from laminar to turbulent flow in pipes occurs at Re between 2000 and 4000.
Re = VD/v
Where: v, the kinematic viscosity of air at sea level is 1.6 x 10-4 ft /sec.
For a 4 inch pipe, this gives a transition velocity of 1 to 2 feet per second.
For fully turbulent flow, hf = f x (L x V2)/(D x 2 x g)
Where:
hf is the head in feet of air (which must be transformed into inches of water).
f is a friction factor which is a function of pipe roughness and other parameters.
L is the length of the pipe.
V is the velocity of fluid flow.
D is the pipe diameter.
Re is the Reynolds number.
The pressure drop h is given in feet of air in the Darcy-Weisbach equation may be converted to inches of water by multiplying by 0.0147.
Solving for head loss in inches of water for one foot of pipe yields the following:
Head loss (inches of water) = 0.0147 x 0.03 x 1/D x V2/64 for 4 inch pipe, this yields 5.7 x 10-9 x v2 per foot
The cross sectional area of a 4 inch pipe is 0.09 sq ft, so assume 30 CFM flow for 3 people, will require a velocity of 344 ft per minute.
344 squared times 5.7 x 10-9 = 0.00081 inches of water column per foot.
For the calculation of pressure drop, the equivalent pipe length should be used. This means that 10 times the diameter (in feet) of the pipe should be added for each elbow and size transition to be used.
Assume 100 ft pipe and 5 elbows
~0.16 inches water head required for a 30 CFM fan
WARNING
Don't forget fresh maybe required for cooking and heating.
Consider CO and O2 monitors
Many utilities have rebate or assistance programs to implement these systems. Tax breaks or incentives for the solar, as well, not to mention depreciation.