Anchoring to Concrete - Large Shear Force
I am working on designing several large brackets to anchor to an existing concrete structure. The brackets are anchored to a wall near the top edge with design loads ranging from 50 kip, 100 kip, and 200 kip. Load is applied at approximate 12" eccentricity to the face of wall. Anchors must resist tension and shear. I am leaning towards design with a shear key to transfer the shear load; as I cannot get reasonble anchor bolt groupings and associated bracket size using bolts to transfer shear. Some contention at that juncture because we do have evidence of older designs which simply used anchor bolts to transfer shear force.
Design specification is to use post installed adhesive anchors. Cannot thru-bolt the anchorage.
The design work is preliminary at this point and we do not have existing drawings to indicate existing wall reinforcing.
Current design references are AISC Design Guide 1, Design of Monopole Baseplates, and Appendix D.
Does anyone have any other strategies to tackle this situation? Using Appendix D really seems to limit the shear breakout condition. Looking back at older PCI design guides it appears they could readily resist 100 kip shear loads with embedded nelson studs. I know this topic has been discussed before just seeing if anyone has any updates or thoughts. Also just two points of clarification below. (Thinking out loud)
Point of clarification:
1.) It will always be conservative to simply use the bolt group moment of inertia in determing the bolt forces rather than performing an elastic analysis of the anchor bolts using a reinforced concrete beam analogy. Just looking for a confirmation.
2.) I have also seen calculations performed where engineers assume the baseplate pivots about an edge with a linear strain distribution through the anchors; this would produce unconservative results.
RE: Anchoring to Concrete - Large Shear Force
I'd also be concerned with the top of the wall failing in flexure as the vertical wall reinforcement may not be developed past the point of cracking.
Supposedly, older bolt methods are not as accurate as ACI 318 App. D. However, App. D. is quite vilified by many engineers - some I know choose to ignore it because they say it is way too conservative.
For the size of loads you have, I'd wonder if a hanger plate assembly, draped over the top of the wall might take the shear. You'd still have the moment/tension forces to take in the bolts.
What will the bracket support? Steel beams?
Can you use a saddle type connection with stiffeners? This would mean that your shear is in bearing on top of the wall and the stiffeners will take out the moments.
Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
I agree about Appendix D regarding large anchor forces, if you call Williams or DSI they can satisfy these requirements; it just conflicts with Appendix D.
Grad student performed multiple tests of multiple anchor configurations and compared the results to App. D calcs. I was surprised to see that App. D was a little UNconservative for anchor groups with large numbers of anchors with overlapping failure cones.
It was a little conservative with fewer anchors and anchors without overlapping failure cones, but I wouldn't be so quick to dismiss it as overly conservative.
I know there are factors for reinforcement but it seems like they have a way too small effect on the numbers compared with what I would think they would provide in terms of helping the capacity.
I understand that fairly shallow anchors wouldn't be helped by a bar some distance away based on the failure cone, etc. but when you deepend your anchors per App D such that the cone would be crossed by, say 8 #5 bars, I just don't believe the failure load that is predicted.
Based on assumptions I can almost talk myself out of a detailed look at shear breakout at the top of the wall.
I am just getting the general question "..well if they did it this way in the past..". Need to jusify an economical and sound solution as we have a multitude of these to install.
I am probably going to require that a shear key is cut and grouted in for the largest anchorages and resist the moment with tension in the anchors.
Less than 80 kip I can manage with a reasonable number of anchors and bracket size.
Use the rod as your shear key, and if deep enough - or through the whole wall though 48 inches is a loooooooooooong way - then use the rod to resist moment as well as shear.
The tests were done with completely unreinforced, uncracked concrete.
You would also require continuous special inspection of the anchor installation and that might make the design less economic.